Laars mini therm soot

Elpisador
Member Posts: 1
in Gas Heating
I have a Laars mini therm jvs125boiler about 10 years old. Had to clean soot 3 times over the last winter. Unit cycles on-off after a few seconds of firing up. Sometimes I get a buzzing sound. Any help is greatly appreciated. Thanks in advance.
0
Comments
-
Combustion is off. Get a competent tech. in there to thoroughly clean it, and with the proper test instruments and get everything set as it should be for best combustion. It is impossible to set a burner correctly by eye or by ear.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
Short cycling and low return water temperature are a couple causes of copper tube boilers sooting up.
Things get worse as the fins plug up.
Get a CO meter near that beast.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Yes, HX probably plugged with soot.0
-
How's your combustion air?0
Categories
- All Categories
- 86.8K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 425 Carbon Monoxide Awareness
- 109 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 105 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 966 Plumbing
- 6.3K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements