Advice on a Kn Series boiler

RayWohlfarth
RayWohlfarth Member Posts: 1,613
A friend called and said they were having issues with their Kn series boiler at his church. The loop was over heating but the temperature readout on the boiler read much lower. In this instance, the water temperature was 147 degrees and the readout read 34 degrees. There was no lockout. The manufacturers rep checked it out and said it was working fine but couldn't understand why the loop overheated. My friend checked the sensor resistance and it was correct. Have you ever heard of this? I haven't worked on many of these boilers. Thanks in advance

Ray Wohlfarth
Boiler Lessons

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,105
    34 degrees makes no sense at all, unless somehow the thing is reading in Celsius -- and even then it seems low. So my money is on either the sensor, the sensor wiring, or the electronic widgets which interpret what the sensor is reading.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    Sylvain
  • RayWohlfarth
    RayWohlfarth Member Posts: 1,613
    Thanks @Jamie Hall
    Ray Wohlfarth