Oil Burner Running Rough
Marco12
Member Posts: 1
in Oil Heating
I have a WeilMclean boiler with a Carlin EZ-1HPW burner. The Nozzle is a .75 60B. The boiler sounded like a big truck running. I replaced the main oil filter, cleaned the flue, checked the chimney, Cleaned the boiler and cleaned the Nozzle (Nozzel had "soot" on it) and electrodes. No one near me had a new nozzle in stock so I had to order. The flame looks good.
I am thinking pump strainer next.
I am thinking pump strainer next.
0
Comments
-
-
-
-
-
My guess is, they cleaned the outside of the nozzle. But that can be problematic.Big Ed_4 said:You really can't take apart and clean a nozzle below 1.25 ...
The solvent, soap or cleaning agent used can cause debris to find its way to making a scratch on the finely machined orifice surface. Touching the cindered filter strainer with any dirt in or on it can force debris thru the filter and end up lodged in the tangential slots or orifice of the nozzle. Never clean a Nozzle smaller than 1.25 GPH, and avoid cleaning nozzles below 2.00 GPH. It just ain't worth it
Once you get the proper nozzle, you will need to check the fuel pump pressure. after the fuel pump pressure is correct for the application you need to follow the instructions for adjusting the burner from this Instruction manual: https://carlincombustion.com/wp-content/uploads/MNEZ123-100923-r3b.pdf
Pay particular attention to the important information on page 15 of the manual. In Particular the item that I put a Red check mark on
If you are a DIY burner mechanic, you will need a Combustion analyser, smoke tester and draft gauge or manometer that can measure air pressure down to 0.01" water column (which is about 0.000 361 272 918 27 PSI). Really sensitive pressure/vacuum gauge.
I spent over $1500.00 for my last combustion analysis kit, over 10 years ago. But if you are going to do this you need the proper tools. Without those tools you should not touch the FIRE that is basically burning in the middle of your home!
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
@Marco12 , where are you located? We might know someone who can help. That boiler needs to be opened up and inspected, and cleaned if necessary, before tuning the burner. You might find something like this:
https://forum.heatinghelp.com/discussion/188633/soot-vac-was-heavy-when-i-finished-this-one
This one was running a bit rough too, and you can see why.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting2 -
@EdTheHeaterMan , said
. Never clean a Nozzle smaller than 1.25 GPH, and avoid cleaning nozzles below 2.00 GPH. It just ain't worth it
In a perfect world I would agree. But if it's 2:00 am and you don't have another nozzle or the right nozzle you do what you gotta do to get the heat back on.
I have cleaned many nozzles in a pinch and would always go back with a new nozzle especially on the small nozzles.
I had a school once with old Power Flame burners that used a Steinen 90 SS nozzle they are no longer made. Substituting different MFG nozzles NG could not get a good combustion test although with the Steinen nozzles it was fine.
Every year when I cleaned them I replaced the nozzle strainers, oil filters and pump strainers.
Then I moved into the office and they had another "tech" take over the oil stuff. I specifically told him about the nozzles........he didn't listen and threw them out.
2 months go by and were getting calls for smoke and soot. They suffered with it until they finally asked me if I could take a look. We tried different nozzles, different spray angles and pump pressures.
They just wouldn't run without the 90 deg Steinen. Ended up changing the burners. Too bad because they could have got some more years out of them. But those were like 6:00 gph nozzles.
My moto is never throw anything away until you know the replacement works.4
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 97 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 929 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements