Considerations for expansion/contraction of PEX run along joists?
The hot water line shown in these pictures is expanding due to temperature increase. It's about 20 feet long.
The pipe is deflecting upwards and downwards from the straight line when it was attached. Is there any worry about abrasion in this scenario? Should there be an expansion/contraction loop at the end of this run to take up the slack instead?
The pipe is deflecting upwards and downwards from the straight line when it was attached. Is there any worry about abrasion in this scenario? Should there be an expansion/contraction loop at the end of this run to take up the slack instead?
0
Comments
-
There should indeed be an expansion loop. Further, on a hot water line, my preference has always been to lay the pipe in a trough, lying free. Otherwise, over time, it will sag.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Throw a few more Talon hangers up there you will be fine. By code a hanger on pex every 30"
0 -
Every 18 to 24 inches is best for hanging pex. especially on the hot water piping. Usually the closer together the hangers the better.
0 -
The red hot would be nice to have insulated. That would save limit heat loss and handle any expansion noise. Shouldn't need and expansion loop in that short run.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
A trick I've used is to cut small pieces of 3/4" plywood and use those as standoffs under the talons. This gives room for 3/4" wall insulation to go on the pipe. The PEX will move less, because of the insulation and will not rub on the wood, so should have a longer life.
Yours, Larry0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements