Pipe Pitch and Pipe Insulation

Steve_211
Steve_211 Member Posts: 49
I know that the steam return has to be pitched. How much per linear foot and can it be pitched too much or it doesn't matter? Regarding insulation, I insulated the main. Should the return be insulated too or that doesn't matter?

Comments

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,401
    edited March 19
    Minimum is 1" per 20 feet. Yes, insulate the return.
    And you can pitch a return pipe as much as 90° from horizontal. So no, you can not pitch a return too much. But if you have a horizontal wet return (below the water line), and it has only the minimum pitch, you will want to make provisions to flush that pipe from time to time. Lots of muck, sludge and other nasty gunk, (gunk is a technical term) will spend lots of time reducing the flow of return condensation back to the boiler.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    PC7060
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,492
    Depends what the return temp is. Payback is probably not worth the insulation cost. I would concentrate on any pipe with steam in it.
  • Steve_211
    Steve_211 Member Posts: 49
    You advise, EdTheHeaterMan, to insulate the return. Initially, I didn't see the efficacy in doing that since the return is not carrying steam to the radiators, but returning condensate back to the boiler.

    EBEBRATT-Ed, you say it depends on what the return temp is. Since the return returns condensate water back to the boiler, wouldn't it not matter, in fact, be better if the return wasn't insulated as this would expedite any remaining steam to condense back to water to return back to the boiler?
  • Jamie Hall
    Jamie Hall Member Posts: 24,872
    Wait. Are we talking a dry return here, or a steam main extension? If it's a steam main extension, if should be insulated. If it's a dry return, it should never have steam in it -- and doesn't need insulation.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Steve_211
    Steve_211 Member Posts: 49
    To Jamie Hall: All the pipe from the riser off the header had insulation on it. Years ago, I removed the pipe insulation from the last radiator takeoff back to the boiler (the return) on my one pipe system. Was this OK?
    What would cause the return to have steam in it and how does one determine that there is steam in it?
  • Jamie Hall
    Jamie Hall Member Posts: 24,872
    Usually a one pipe system doesn't have a true return, but an extension of the steam main which is there to get condensate back to the boiler. It really should be insulated, but it's not a tragedy if it isn't. You will only get significant steam in it if there is a vent on it somewhere down the line -- and you can easily tell -- if it gets steam hot, or nearly so, it's accepting steam and insulation will save a bit. Not much...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,401

    As far as insulation goes, it depends on the quality of the studio construction. I hate it when you are trying to make a recording and you get the noise of a firetruck siren going by, on you demo tape

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    Intplm.ChicagoCooperatorLong Beach Ed
  • Intplm.
    Intplm. Member Posts: 2,200
    Oh @EdTheHeaterMan , is that the circle of fifths on that pitch pipe? Maybe we can get the steam whistle pitched to a tune? LOL.
    EdTheHeaterManChicagoCooperator
  • Steve_211
    Steve_211 Member Posts: 49
    To Jamie Hall: The steam main extension (the not so true return) does have a vent on it, a Gorton Air Eliminator #1, at the end where it drops back to the boiler, near the hartford loop. When the system is cool, the valve in the vent is open, as I hear it make noise when I knock on it. When the system is operating, the valve in the vent is closed as it doesn't make noise when I knock on it and it's hot. Is the vent necessary? Can it be removed and the venting of the system be adequately handled by the vents on the radiators?
  • Tuggy
    Tuggy Member Posts: 71
    Steve_211 said:

    Can it be removed and the venting of the system be adequately handled by the vents on the radiators?

    Wouldn't that be considered a main vent and therefore should not be removed?
    ChicagoCooperator
  • KC_Jones
    KC_Jones Member Posts: 5,840
    Steve_211 said:

    To Jamie Hall: The steam main extension (the not so true return) does have a vent on it, a Gorton Air Eliminator #1, at the end where it drops back to the boiler, near the hartford loop. When the system is cool, the valve in the vent is open, as I hear it make noise when I knock on it. When the system is operating, the valve in the vent is closed as it doesn't make noise when I knock on it and it's hot. Is the vent necessary? Can it be removed and the venting of the system be adequately handled by the vents on the radiators?

    Definitely don't remove the main vent. Balance starts with main venting, without it balance becomes and issue, as well as speed of filling the mains.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • Jamie Hall
    Jamie Hall Member Posts: 24,872
    That vent, as the folks above have said, is actually the main vent for that whole line of piping. You very much need it. In fact, if it's just a #1, I would not be surprised if the system could benefit from a #2 instead.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Steve_211
    Steve_211 Member Posts: 49
    To KC_Jones: Point taken.

    To Jamie Hall: Point also taken, and your suggestion to upgrade to a Gorton #2. I will definitely be doing that. Also, being that I removed the insulation from the extension of the steam main, would it be advisable to re-insulate it?
  • Jamie Hall
    Jamie Hall Member Posts: 24,872
    Yep.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England