Intermittent steam (water) hammer
briggs
Member Posts: 11
Hello, We're having an intermittent problem of hammer in a riser from basement to second floor radiator. See attached drawing.
Hammering may occur on boiler start up or shutdown. Sometimes it is mild hammering, sometimes it's rather severe.
Boiler Pressure Troll is adjusted to it's lowest setting.
Boiler operating at between 5 & 7 lbs.
Sight glass is 7" long & water level is approx 3" from bottom during operation. No water droplets in the glass above water line.
This is a 2 pipe system & riser pipes are buried in the wall with no access.
What's causing the hammering & what can we do to sop it?
Hammering may occur on boiler start up or shutdown. Sometimes it is mild hammering, sometimes it's rather severe.
Boiler Pressure Troll is adjusted to it's lowest setting.
Boiler operating at between 5 & 7 lbs.
Sight glass is 7" long & water level is approx 3" from bottom during operation. No water droplets in the glass above water line.
This is a 2 pipe system & riser pipes are buried in the wall with no access.
What's causing the hammering & what can we do to sop it?
0
Comments
-
"Boiler Pressure Troll is adjusted to it's lowest setting.
Boiler operating at between 5 & 7 lbs."
That makes no sense. I don't know of a pressuretrol which can't be adjusted down to about 0.75 psi cutin/1 psi differential.
So do it.
5 to 7 psi is MUCH too high. If it hasn't already trashed your vents and traps, it will.
Now on the hammer. You show two horizontal sections of pipe. My guess wold be that one of them -- or more than oone -- has gotten slightly off pitch. Wouldn't take much.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
Is the pigtail between the pressuretrol and the boiler clean, also the opening into the boiler itself? The pressuretrol cannot do its job if these are clogged.—
Bburd0 -
-
Gentlemen, Thank you for your comments. Will follow up on them. Very helpful.Mr. Hall, Will go back to pressuretrol for proper adjustment. Ed, What are your thoughts on using 1/2'' copper? Why won't it work on a radiator?0
-
1/2” copper doesn’t have sufficient volume to deliver steam while allowing condensate to return back beneath the steam. Steam radiator pipes are never less than 1” unless a very special two pipe vacuum vapor system. There’s simply not enough volume in the pipe for supplied steam to not get into a hammer fight with returning condensate in a one pipe steam system.0
-
Ok Waher, This makes sense. Thanks for the explanation!0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements