Flow Control Valve

Mikb1957
Member Posts: 12
I'm changing the upstairs zone on my hydronic heating system to radiant floor heat. It used to be baseboard. The B&G F00200 flow control valve needs to be replaced, I was wondering if there is a specific valve I should use with the system. It's a five zone manifold, each with a zone valve.
0
Comments
-
Is there going to be a mixing valve involved with the radiant, and a separate zone pump?
If so the check in the circ should be adequate.
Or a basic hydronic spring check, serviceable like this.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
I hope there will be a mixing valve and separate zone pump! Otherwise you are going to overheat that floor...hot_rod said:Is there going to be a mixing valve involved with the radiant, and a separate zone pump?
If so the check in the circ should be adequate.
Or a basic hydronic spring check, serviceable like this.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Yes, separate zone pump with check valve and a mixing valve. I'll just eliminate the old flow valve. Thanks for the info, very helpful.0
Categories
- All Categories
- 86.9K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 109 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 105 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 977 Plumbing
- 6.3K Radiant Heating
- 387 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements