Flow Control Valve

Mikb1957
Mikb1957 Member Posts: 12
I'm changing the upstairs zone on my hydronic heating system to radiant floor heat. It used to be baseboard. The B&G F00200 flow control valve needs to be replaced, I was wondering if there is a specific valve I should use with the system. It's a five zone manifold, each with a zone valve.

Comments

  • hot_rod
    hot_rod Member Posts: 23,270
    Is there going to be a mixing valve involved with the radiant, and a separate zone pump?
    If so the check in the circ should be adequate.

    Or a basic hydronic spring check, serviceable like this.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2
  • Jamie Hall
    Jamie Hall Member Posts: 24,727
    hot_rod said:

    Is there going to be a mixing valve involved with the radiant, and a separate zone pump?
    If so the check in the circ should be adequate.

    Or a basic hydronic spring check, serviceable like this.

    I hope there will be a mixing valve and separate zone pump! Otherwise you are going to overheat that floor...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    mattmia2
  • Mikb1957
    Mikb1957 Member Posts: 12
    Yes, separate zone pump with check valve and a mixing valve. I'll just eliminate the old flow valve. Thanks for the info, very helpful.