Flow Control Valve

Mikb1957
Member Posts: 12
I'm changing the upstairs zone on my hydronic heating system to radiant floor heat. It used to be baseboard. The B&G F00200 flow control valve needs to be replaced, I was wondering if there is a specific valve I should use with the system. It's a five zone manifold, each with a zone valve.
0
Comments
-
Is there going to be a mixing valve involved with the radiant, and a separate zone pump?
If so the check in the circ should be adequate.
Or a basic hydronic spring check, serviceable like this.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
I hope there will be a mixing valve and separate zone pump! Otherwise you are going to overheat that floor...hot_rod said:Is there going to be a mixing valve involved with the radiant, and a separate zone pump?
If so the check in the circ should be adequate.
Or a basic hydronic spring check, serviceable like this.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Yes, separate zone pump with check valve and a mixing valve. I'll just eliminate the old flow valve. Thanks for the info, very helpful.0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 101 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 102 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 934 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.3K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements