Zone Valve Issues On New Boiler
Rizz861
Member Posts: 62
in Gas Heating
So this particular boiler has 3 zone valves (caleffi) and a Taco 007 F5 pump. The HO is experiencing water hammer only when zone two is closing. There were no CV I could see and the ZV and pump are the right direction. ZV are on supply. Any ideas?
0
Comments
-
Is the pump being controlled by the end switch? The pump should stop spinning when the zone valve starts to close. Tubing that is not secured tightly can cause some noise also when a valve closes.
Where are you located?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
-
Installing a Delta P pump would help. Grundfos 15-55 or the like.
0 -
Are you still experiencing hammer? Which valve do you have?
contact Taco at 401-942-8000 and ask for tech support.Joe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions0 -
What is water hammer? Is it the momentum of a flow of water crashing against a stop? hmmm
What is that telling you? Maybe the flow in that particular zone is excessive? Maybe the zone valve is closing too fast? Honeywell ZVs have two return springs in which case I have removed one spring with success in reducing water hammer allowing the valve to close slower. Caleffi may only have one spring, I don't know.
I always use balancing valves not only to balance flows thru the system but to regulate the flow thru a given circuit. I have also put a washing machine water hammer air arrester on the offending zone's hose bibb with success.0 -
@Big Ed_4The zone valve should be piped on the opposite end from the circulator locationWhy is that? Inquiring minds want to know. In an open sys flow has a relationship to pressure. The more pressure the greater the flow. In a closed sys the flow is the same in every part of the circuit. That's what I thought, but I may be wrong on that. I am interested in what you think.0
-
Almost. The ringer in the deck is that if a pump stops quickly enough it generates a negative pressure -- not flow -- wave in the pipe, and that can be a source of hammer. If a valve closes quickly against flow, it will create a positive pressure wave, and that can hammer. I don't think it really makes a whole lot of difference, though, whether the pump and the zone valve are close together or not...HomerJSmith said:@Big Ed_4
The zone valve should be piped on the opposite end from the circulator locationWhy is that? Inquiring minds want to know. In an open sys flow has a relationship to pressure. The more pressure the greater the flow. In a closed sys the flow is the same in every part of the circuit. That's what I thought, but I may be wrong on that. I am interested in what you think.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
With a spring loaded zone valve , it is best to add resistance between the valve and pump . A buffer , Helps to prevent this type of call ..
There was an error rendering this rich post.
0 -
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements