Proper Pressure Settings for Residential Steam Boiler
ups3341
Member Posts: 2
I got Burnham SIN6LNI-LE2 Steam Boiler, i found out it When the thermostat calls for heat, the boiler has been running for 25-35 minutes. Then, it shuts off. My 3 floor doesn't have heat or got some. I think pressuretrol isn't setup correct because i know the contractor touch few times, at beginning the heat turned on for more than an hour,,
Any help is greatly appreciated! Many thanks.
Any help is greatly appreciated! Many thanks.
0
Comments
-
That's way too high. Residential steam should never need more than about a pound.
If the steam does not distribute properly, there are plenty of Steam Guys on here who can help you. Where are you located?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
The lowest pressure that is needed to get the steam to the radiators. The Empire State building only needs 2 PSI. How far away from the boiler is your farthest radiator, compared to 100+ floors of the ESB?
Is this a one pipe steam system? Are all your air vents working? You need to get this book... We Got Steam Heat Available in the store on this site or on Amazon.comEdward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
It should never need more than an ounce. But the pressure controls don't really let you set it that low.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Adjust the settings with the two small screws on the top left side of the grey pressuretrol box.
Set the diff to 1 and the main to 1.5 for a cut-in pressure of 0.5 PSI and a cut-out of 1.5 PSI.
Without a low pressure gauge you won't be able to tell if the pressuretrol is accurate to those settings, but it will get you in the ballpark.1 -
-
-
Thank you for everyone's advise, I put main 2 and different 1.5 is working..-1
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements