Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
This Friday's case, the case of the lost heat call
RayWohlfarth
Member Posts: 1,656
In this case, the customer called and said all 4 boilers were off. The boiler sequencing was done by the building's digital control system, something I hate doing. I would rather they send us an enable or disable signal and let us control the boilers but I digress. When we arrived, the building and hydronic loop was cold. All 4 boilers were off. While there, the first boiler started and stopped after a few minutes. I noticed the call for heat light was not lit on the Rib Relay. A few minutes later, the light light followed by the boiler. It shut off after a few minutes. As usual, I will let you know Friday at 6am EST. Thanks
Ray Wohlfarth
Boiler Lessons
Boiler Lessons
0
Comments
-
-
-
-
Installed in the winter, now it is warmish out and triggering warm weather shutdown. Trying to make DHW only and didn't put in the right logic to still allow that when it is warm out.0
-
Wow lots of great guesses. I love that about our industry. Just when I think I have it figured out, a new twist is added. The problem was the boiler heated so quickly, it would shut off on the supply water temperature. The supply temperature sensor was really close to the lead boiler outlet. Since it was milder weather, the loop didnt need much heat. The solution was to relocate the sensor to the return and everything worked great.It's almost like the Karma Gods say, That Ray is pretty cocky. Let's throw him a curve. LOL here is the link to the video. Thanks everyone. https://youtube.com/watch?v=zS2RvBQCWxIRay Wohlfarth
Boiler Lessons3 -
Hi Ray,
It's been a number of years since we met at the Wetstock at the General Society and I showed you the boilers, etc. I'm a control system freak, hence my nickname (thanks Dan!) of the WireNut, of which I'm very proud! In any case, I really enjoyed this detective case and the way you taught that control "engineer" a lesson. Too many "engineers" design stuff but have no experience in the field they design for. Every engineer should work in the field first and learn their business first hand and, especially, to understand that things will have to be serviced. No matter how clever your design and features, if it can't be installed without issue and more importantly, serviced in the future, it's junk!
All the best and thank you for these greatly informative cases.
Alex aka WireNut"Let me control you"
Lost in SOHO NYC and Balmy Whites Valley PA0 -
@The Wire Nut I remember meeting you Thanks for the tour. I dont like being petty on a job and never embarrass anyone in front of another person but in this case i made an exception. Funny thing is I used to be a control tech, spending several years with Johnson Controls. Thanks for watching Alex!Ray Wohlfarth
Boiler Lessons1 -
@RayWohlfarth If you are ever back in the city, and want to continue the tour, just let me know!
I prefer wires to pipes, though it's almost the same, just moving electrons instead of molecules!
Thanks for the detective cases, brings me back to my Sherlock Holmes days!
Alex"Let me control you"
Lost in SOHO NYC and Balmy Whites Valley PA0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements