vxt-24 water feeder displaying code

nytech28
nytech28 Member Posts: 70
I came across this boiler which I visually checked, with waterfeeder displaying "26h" see pictures, not sure what code means , it's keeping the boiler off any suggestion would help what the display means .thanks 

Comments

  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,204
    492 gallons of feed water. You are reading it upside down. And the water feeder does not have the ability to turn your boiler on or off
  • Jamie Hall
    Jamie Hall Member Posts: 24,727
    I'd have to go find my manual, but I have a recollection somewhere that the VXT will lock out if it senses too much water being fed in too short a time -- and since 492 gallons is about what a residential boiler installed in 1890 might have used by now, if all is well, it may have done that -- and the low water cutout is likely what is keeping your boiler from firing.

    You have a problem, but it's not the VXT feeder. That's just the messenger.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,204
    Will display "LOC" (I think) if it locks out. 
  • nytech28
    nytech28 Member Posts: 70
    it's stock at 492 dispaly
  • Jamie Hall
    Jamie Hall Member Posts: 24,727

    Will display "LOC" (I think) if it locks out. 

    You're right. I just looked it up...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • 109A_5
    109A_5 Member Posts: 1,589
    edited February 4
    Hello @nytech28,
    26h or 26 HEX is one of the many error messages that you are reading the display upside down. Seriously, if it is 'stuck', maybe it is just glitched. Power it down for a minute or so then see how it behaves. See if it will reset to Zero and work properly.





    https://hydrolevel.com/wp-content/uploads/2021/06/VXT-24-Instructions-web-0321.pdf


    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • nytech28
    nytech28 Member Posts: 70
    ok thanks