2 Radiators Not Heating 2 Pipe
mugen
Member Posts: 11
Have a very strange problem at a customer's house. Numerous companies have been there now its my turn to be schooled. Here's the problem.
2 radiators one on second floor and one on third don't get hot. All other radiators get hot. 2 pipe Hoffmann DL system. The last companies replaced all traps.
When I arrived I took radiator out I could hear gurgling in pipe. Blew down pipe with nitrogen after a little while steam cane out and both radiators got hot. The customer called and said when heat shuts off it didn't get hot again. Went back today removed radiator gurgling again. Removed cross over trap from main and return line blew line from radiator nitrogen came out of third floor radiator and out of main where I removed trap. It makes no sense.
The pipe that is supplying steam to the riser that goes to the problem radiators is not insulated and in garage and pitched slightly away from main and riser is last on pipe. I feel this might be the cause. To much condensate in this pipe causing issue with steam. Would this be plausible.
Any suggestions would be appreciated.
2 radiators one on second floor and one on third don't get hot. All other radiators get hot. 2 pipe Hoffmann DL system. The last companies replaced all traps.
When I arrived I took radiator out I could hear gurgling in pipe. Blew down pipe with nitrogen after a little while steam cane out and both radiators got hot. The customer called and said when heat shuts off it didn't get hot again. Went back today removed radiator gurgling again. Removed cross over trap from main and return line blew line from radiator nitrogen came out of third floor radiator and out of main where I removed trap. It makes no sense.
The pipe that is supplying steam to the riser that goes to the problem radiators is not insulated and in garage and pitched slightly away from main and riser is last on pipe. I feel this might be the cause. To much condensate in this pipe causing issue with steam. Would this be plausible.
Any suggestions would be appreciated.
0
Comments
-
There is a low point somewhere in that piping that is trapping water and blocking the steam. Find it and re-pitch it.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Is there a drip on the end of that pipe which is sloped away? If there isn't, there needs to be one... either that or a water seal loop to the dry return at that location. Assuming the dry return exists... and slopes back to the boiler... despite the best efforts of some engineers, water only flows down hill.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements