EK-1 2000 lockout ?
Caboose
Member Posts: 4
EK-1 2000 installed in 1998, 3 zones + DHW - well maintained, serviced annually; has performed all these years with NO problem, but in past month about once a week has had 3 events of 140 degree Flashing on Manager with Monitor Light ON, screen says "No flame" but no error code, reset and resumes normal function (until next event). Technician (has provided our service for 20 years and knows/installs EK) advises because of problem and age, entire system should be replaced (boiler, tank, pipes, venting) - I asked if it could be a part, etc that is malfunctioning and could be fixed instead of having to rework the entire system, but he said he couldn't be sure which part it would be. I would appreciate Forum's thoughts. Thank you.
Did he call Tech Support while there?0
If the unit is going off on reset the problem would be at the burner. If it has the Carlin primary control you can hit the down and right arrow at the same time to get into the details on the fault that is causing the lockout. It would also be a good idea to check the overfire draft to make sure that the unit isn't being shut down by the blocked vent/puff switch on the front of the boiler. If your service provider contacts our tech support team when they are onsite, we will be happy to help diagnose this issue.John Ringel Energy Kinetics2
Thank you. I will ask him to follow up with you.0