Venting plug?

metrosilo
metrosilo Member Posts: 34
Hey guys
just wanted to see what some of you do to plug the hole you use when you do a combustion analysis on cpvc venting. I’ve seen the foil tape. I’ve seen the high temp silicon. 
If you are doing an analysis regularly, is there something you can put in the hole that you can take out and out back when your done?

Comments

  • yellowdog
    yellowdog Member Posts: 169
    Thread it and put a stainless steel plug in it.
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,380
    I am going to take a wild guess here and say that is a category IV vent. That’s a condensing positive pressure vent. It must be sealed so that flue gas doesn’t leak into the boiler room. Especially if the boiler room is inside your home.


    I like the threaded plug idea. Add a high temp sealant

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    mattmia2
  • pecmsg
    pecmsg Member Posts: 5,291
    Or plastic. 
    mattmia2
  • hot_rod
    hot_rod Member Posts: 23,392
    A 1/4 or 3/8 NPT thread with a PVC or stainless plug are a common way to seal that. Some red RTV silicone for extra insurance. You need to tap the hole first, you can't just force a NPT fitting into the hole.
    Look up the hole size required for the tap size you decide on.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mattmia2
    mattmia2 Member Posts: 10,933
    If you had drilled a smaller hole you could probably just use a 3/8" ss or nylon bolt with some tape or dope.(obviously tap the hole)
  • Bob Harper
    Bob Harper Member Posts: 1,091
    System 636 is listed in Canada. I'm not familiar with what they allow. In the US, there is a battle going on regarding a listing for Sch40 PVC. Regardless of the listing, mfrs such as Charlotte Pipe have stated don't use their products for combustion venting. Fernco says don't use their flexible pvc couplings but sells them to mfs of power vented water heaters. If you drill and tap the pipe you can insert either a nylon, pvc, or ss plug.
  • mattmia2
    mattmia2 Member Posts: 10,933
    It is possible that Fernco is running a different plastic formula when then sell their fittings to boiler manufacturers.
  • Intplm.
    Intplm. Member Posts: 2,196
    Screw a machine screw in the hole.
    You don't even need to take a threading tap to the plastic hole. The machine screw will do it.
  • pecmsg
    pecmsg Member Posts: 5,291
    From the look of the picture I don’t think they make a zap screw that large.