HTP UFT error 11 help
joncroteau
Member Posts: 26
I’ve started a new thread as I have highjacked my previous thread with a different issue.
My HTP UFT80 was installed in late 2016. I am just recently dealing with a persistent but intermittent error 11 (no ignition). Coincidence or not, this began after my gas company came out for a leak at my house regulator. I believe I have worked through all of the steps outlined in the manual but the error still happens. It happened when it was around 15f outside and also just now while it is 39F outside. I’ve completed the steps below:
LP line pressure to the valve was set to 10.9
new ignition was installed
combustion test came back within specs on low and high fire
burner and heatx were cleaned
both vents have no restrictions on air flow
rubber flapper in blower is in tact
condensate trap and lines are clean
Tech support said to clean the burner and that would probably solve it. I did but it is still throwing errors.
new ignition was installed
combustion test came back within specs on low and high fire
burner and heatx were cleaned
both vents have no restrictions on air flow
rubber flapper in blower is in tact
condensate trap and lines are clean
Tech support said to clean the burner and that would probably solve it. I did but it is still throwing errors.
Does anyone have any tips or information on what direction to go with this next?
0
Comments
-
I had one of these that was making me pull my hair out for the same error code. If I'd loosen that nut on the "mixer" that brings the gas in and let it suck air, it'd light every time. I threw parts at it 10 different times and essentially had a new boiler but the same issue persisted. Then I drilled a 1/2" diameter hole in the rubber intake boot inside the cabinet, and 3 years later it's never done it again.0
-
GroundUp said:I had one of these that was making me pull my hair out for the same error code. If I'd loosen that nut on the "mixer" that brings the gas in and let it suck air, it'd light every time. I threw parts at it 10 different times and essentially had a new boiler but the same issue persisted. Then I drilled a 1/2" diameter hole in the rubber intake boot inside the cabinet, and 3 years later it's never done it again.
0 -
two things that i would do that i have done in the past. First, use compressed air to blow out the mesh burner. To solve one problem I had I was recommended by engineering of the boiler to blow the mesh burner out with 95 psi of air. problem solved.
if problems persist i would inspect the mixer and the air damper. i'm not to familiar with this boiler but the air damper looks like an item that could give you nuisance lockouts.0 -
Make sure the screens on the intake and exhaust didn't get clogged or maybe ice or water ended up somewhere in the vents when it was shut down because f the gas problem.0
-
mattmia2 said:Make sure the screens on the intake and exhaust didn't get clogged or maybe ice or water ended up somewhere in the vents when it was shut down because f the gas problem.0
-
Here’s another current thread that deals with the ignition issue:
https://forum.heatinghelp.com/discussion/195923/htp-boiler-short-cycle#latest
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.1 -
Ironman said:Here’s another current thread that deals with the ignition issue:
https://forum.heatinghelp.com/discussion/195923/htp-boiler-short-cycle#latest0 -
I copied the wrong link - my apologies.
Im glad the adjustments improved your situation.
Here’s the correct thread:
https://forum.heatinghelp.com/discussion/195772/htp-uft-199-boiler-lp#latest
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.1 -
Thank you. I thought I had seen this potential remedy in here somewhere.0
-
I have no idea what the science is, I just know it fixed the problem. I'm referring to the nut that you have circled in the above photo. Yes it was intermittent and sometimes I could recreate it, sometimes not. There is a rubber "elbow" fitting that comes from the intake pipe inside the cabinet, to the inlet side of the mixer. I drilled a hole in the bottom of it, right near the elbow in the rear of the cabinet where it turns to come forward.1
-
GroundUp said:I have no idea what the science is, I just know it fixed the problem. I'm referring to the nut that you have circled in the above photo. Yes it was intermittent and sometimes I could recreate it, sometimes not. There is a rubber "elbow" fitting that comes from the intake pipe inside the cabinet, to the inlet side of the mixer. I drilled a hole in the bottom of it, right near the elbow in the rear of the cabinet where it turns to come forward.0
-
Nvm, your original post says you checked it0
-
Quick update on this issue:
After multiple visits by the gas company, I discovered the regulator on the underground propane tank was freezing up. Gas company came out and changed the regulator and did a pressure check. They said they were confident that was my issue. The system has been up and running for 24 hours so far with no ignition lockout.
update #2. Boiler ran for 2 days with no issue. Just got an Error 11 again. Back to the drawing board.1 -
Having this exact issue error 11 and not sure how to adjust the mixture screw. Where exactly would it be located. I'm on a htp uft-199w. Seems it's not getting enough gas to keep lighting. After a few on off attempts and letting the unit sit for a bit it seems to fire up but only after a while.
Need help asap if anyone can direct me to which is the mixture screw.
Thank you
Edit:
I figure from the diagram from the manual where the screws are. However, I am wondering which one is needed to be adjusted to turn up the gas mixture. The inlet screw or the outlet. Inlet obviously makes sense but when adjusting the inlet screw does the outlet screw get adjusted the same also?
Thanks
Pictures attached
0 -
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements