No Heat

brrogers
brrogers Member Posts: 2
edited January 21 in Gas Heating
Boiler gas valve was replaced and it flashes code 6, "Internal Fault, gas valve circuit," what else could it be?? 

Weil Mclain CGa Series 2 boiler

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,727
    Why does it need to be anything else? The code is referring to the entire gas valve circuit, not just the valve -- so I'd start checking to make sure the connections are correct and secure...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    brrogersIntplm.
  • brrogers
    brrogers Member Posts: 2
    Jamie , 
    Thank you for replying. We say anything else because multiple companies have been out to look at our boiler with no help. They see no "issue" and are confused too. The boiler runs 12+ hours with no code  then shuts off and starts flashing the code . 
  • 109A_5
    109A_5 Member Posts: 1,589
    Hello @brrogers,
    Did it flash code 6, "Internal Fault, gas valve circuit," before the gas valve was replaced ?
    Was 24 VAC verified at the gas valve?
    A to C - Pilot Valve
    A to B - Main Valve
    If not why was the gas valve changed ?




    If the problem is intermittent, probably a poor connection somewhere, bad crimp, oxidized connector connection, failing solder joint in the control module, etc.

    Troubleshooting charts in manual.
    https://www.weil-mclain.com/sites/default/files/field-file/CGa Series 2 Boiler Manual - date code 12-2012.pdf

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    brrogers
  • ambercontractors
    ambercontractors Member Posts: 17
    I just went through a similar experience, on a Weil Mclain 155 Ultra Series3, called the company tech support they say when lockout reads gas valve fault 99% of the time its the U control, you might have to replace the board.