Furnace seems stuck in lockout mode after power outage
I have a Trane XV90 forced air furnace that seems to be stuck in lockout mode. I'm seeing the error code "two green flashes and then two red flashes," which I think means "open high limit switch." The furnace was working properly until a tree knocked down our overhead electrical service during an ice storm and we lost power. Power is now restored, but now we need to get the heat going. The furnace goes through the motions of starting up but seems to cut out after the warm glow appears in the upper sight glass. (It does not have a pilot light.) It repeats this a few times and then seems to give up. The fan then kicks on and it blows the cold air through the ducts.
I don't see a reset button. I tried resetting it by turning the power off for a minute or two and then turning it back on, but get the same result. Also, the natural gas shutoff valve doesn't have a lever so I'm not a 100% certain it is in the optimal position. I'm including photos below. Does the control board look okay? Is there anything else I can try?
The high limit switch may be a manual reset switch -- or worse, a one shot. Have you located it and checked to see?
Otherwise if there was a voltage surge when the tree interfered, you may have a fried control board.Br. Jamie, osb
If the furnace was working prior to the power outage you can probably rule out the gas shut off valve. What you do need however is a multi meter to check the other components. One possible problem is the hot surface ignitor is not producing the required " heat" for ignition. Without a multi meter we are just guessing.1
I have not been able to locate the high limit switch. I was hoping to find it so I could try a manual reset if there was one.Jamie Hall said:The high limit switch may be a manual reset switch -- or worse, a one shot. Have you located it and checked to see?
Otherwise if there was a voltage surge when the tree interfered, you may have a fried control board.0 -
Initially I thought I smelled gas so I turned the gas shut off valve. I'm not 100% sure I put it back in the correct position. I will try to get my hands on a multi meter.Cooper1957 said:If the furnace was working prior to the power outage you can probably rule out the gas shut off valve. What you do need however is a multi meter to check the other components. One possible problem is the hot surface ignitor is not producing the required " heat" for ignition. Without a multi meter we are just guessing.
If your furnace was firing at the time of the power loss, the heat exchanger had a lot of heat in it, and when it rises up, it causes the manual reset high limit switch to open. I believe if you look between the two bright yellow wires in the picture, you will find a small reset button. Push that and it should refire. Your gas valve shown is open, The two dots on opposing corners of the gas cock show the position of the close off. Parallel to the pipe is open, right angle to pipe is closed.If the high limit is fried, you can bypass it temporarily until you get a new one, but do not leave it bypassed under penalty of death and or fire.3
Thank you very much! You are right, if you follow the two yellow wires, it leads to a small red reset button. I pressed on it, and it didn't feel like it moved at all, and the furnace didn't refire. It makes me think that it had not actually tripped. I guess this switch is called the "flame roll out switch." Is it possible that the "high limit switch" is the one behind the flame rollout switch in the photo below:Mark Eatherton said:If your furnace was firing at the time of the power loss, the heat exchanger had a lot of heat in it, and when it rises up, it causes the manual reset high limit switch to open. I believe if you look between the two bright yellow wires in the picture, you will find a small reset button. Push that and it should refire. Your gas valve shown is open, The two dots on opposing corners of the gas cock show the position of the close off. Parallel to the pipe is open, right angle to pipe is closed.If the high limit is fried, you can bypass it temporarily until you get a new one, but do not leave it bypassed under penalty of death and or fire.
Yes the high limit is the one attached to the furnace with the two screws. Not the one with the reset button. Try jumping the two yellow wires on the HL.
As Mark said this is fir troubleshooting only you can warm up the house if it works but DO NOT LEAVE IT JUMPED>
Can you post a picture of the wiring diagram?0 -
Gas is flowing to our hot water heater and the burners on our cooktop. I can't say for sure whether it is flowing properly to the furnace, although I was told the furnace's gas shutoff valve is in the correct position for gas to flow.109A_5 said:0 -
Thank you very much -- I'd like to try your suggestion. Could you clarify what you mean by "jumping" the two yellow wires?EBEBRATT-Ed said:Yes the high limit is the one attached to the furnace with the two screws. Not the one with the reset button. Try jumping the two yellow wires on the HL.
The wiring diagram on the panel is in rough shape. I'm including that below along with the ones in the installer's guide. I looked online for wiring diagrams for our model, TUY100R9V4W1 (aka UY100R9V4W1),
and haven't found anything yet...
Alix said:
To be more precise, the flashes are actually as follows:mattmia2 said:I'm not sure you're reading the flashes right. Might want to read the manual. Maybe it is only the 2 red flashes and failure to prove flame which sounds more like what's happening.
Green
Green
Red
Red & Green simultaneously
So, a total of 4 flashes, unless the flash of red & green simultaneously counts as more than one.0 -
Hello @Alix,
Do you hear the gas valve click assuming the control board tries to open it ?
With a multi-meter you could tell if the control board is even getting to that point 24 VAC across the gas valve's terminals and you can also test the continuity of the other limits and sensors.
One Pipe System1 -
I definitely hear a clicking sound where the gas valve is located, and around that time I can smell a faint whiff of gas. I'm planning to head out soon to pick up a multi-meter.109A_5 said:Hello @Alix,
Hello @EBEBRATT-Ed, I used a makeshift jumper wire on the high limit yellow wires as shown in the image below, and then powered on the furnace. It continued doing the same thing it has been doing (it goes through the motions of starting up but cut outs after the warm glow appears in the upper sight glass). Also, I did pick up a multi-meter. I guess that's the next thing to try? Or should I try cleaning the flame sensor first?
There is no flame to sense, it isn't getting that far0
Hello @Alix,
Measure one at a time during an attempt to start the furnace, while the hot surface igniter is glowing measure MV COM to MVH then MV COM to MVL to see if any power from the control board is attempting to open the gas valve. I'm not sure if it starts off in Low or High fire.
One Pipe System1 -
The furnace was installed in 2003. Google says Emerson acquired White Rodgers in 1961, but it seems they may not have "merged" until 2015 during a strategic reorganization.mattmia2 said:Was this furnace made after emerson bought white rodgers? If not that board is a replacement and you need to find the instructions for it.
Yes, I've had the blower door closed. Is the safety switch in there something to measure, or might it have a reset button that could be a quick fix?Mark Eatherton said:Is the blower door closed? I think there'a safety switch there too...
The furnace was working properly until a tree knocked down our overhead electrical service during an ice storm and we lost power.I always ask when a incident like this happen, is any thing else in the house acting strangely, burned out light bulbs or something else not functioning properly?
If the neutral wire is disconnected first in the mishap and the phase wires remain connected, you will have 220V going thru everything connected and operating that would normally operate on 110V. It's called a dropped neutral, in which case the board is fried.
As further note, I think that the gas union should be outside of the cabinet, not inside.2 -
The other thing I think of is whether someone ran a portable generator to power the house.HomerJSmith said:I always ask when a incident like this happen, is any thing else in the house acting strangely, burned out light bulbs or something else not functioning properly?
1 -
All the other electrical items in the house are functioning normally after the power was restored.HomerJSmith said:The furnace was working properly until a tree knocked down our overhead electrical service during an ice storm and we lost power.I always ask when a incident like this happen, is any thing else in the house acting strangely, burned out light bulbs or something else not functioning properly?
As further note, I think that the gas union should be outside of the cabinet, not inside.0 -
I did not run a portable generator to power the house after this incident. However, the house does have a generator hookup available, and that may have been used years ago.MaxMercy said:
I think these are your instructions:
https://www.copeland.com/documents/50v54-820-instructions-en-5124596.pdf1 -
Thank you very much everyone for your help! I'm learning a lot as always. The furnace repair person was just here. He said the control board was NOT sending power to the gas valve in HIGH flame/heat (the high heat relay is not working). And he said the furnace had been jumpered to run at HIGH flame/heat at all times. He said the control board DOES send power to the gas valve in LOW flame/heat, so he was able to get the furnace to produce heat, but just in low flame/heat.
He said the power outage could have damaged the control board, and that it would need to be replaced to be able to restore the high heat. Unfortunately, the control board for this unit is apparently only sold as part of a kit with a few other high priced items, and so the kit would cost about one quarter to a third of the cost of a new furnace. He said we might be able to get by with low flame/heat for a while. I wonder if there might be a way to purchase a control board without the kit?0 -
it looks like it comes with an ignitor but i doubt that is the expensive part:
https://www.supplyhouse.com/White-Rodgers-50V54-820-Trane-Replacement-Two-Stage-Furnace-Control-Kit-for-80V-120V-Hot-Surface-Ignition-Variable-Speed-Blower-Motors
Unless they did a much better job on sizing than most installers do, it probably exceeds your heat loss on low fire.1 -
You are all awesome, thanks! Now that I have heat I'm planning to return to the furnace project tomorrow, and I'm sure I'l have lots of follow up questionsmattmia2 said:it looks like it comes with an ignitor but i doubt that is the expensive part:
Thank you very much for this suggestion! I look forward to trying this hopefully tomorrow after I get caught up on work!mattmia2 said:Oh, you might want to trace the wire back from the high terminal of the gas valve to the control board to see if it got spliced in the board transplant and maybe is disconnected somewhere. Look at the connector to make sure the terminal isn't loose in the housing too.
SupplyHouse said that item is discontinued, and that I would need to replace the board and inducer: https://www.supplyhouse.com/Trane-KIT16582-Draft-Inducer-Kitmattmia2 said:it looks like it comes with an ignitor but i doubt that is the expensive part: