Hi,
I had a new boiler installed last year and was having random problems. During the last summer when my boiler was only being used for hot water I didn't experience any issue. As soon as fall came and we turned on the heat we started having issues again. This new issue is that the boiler randomly cuts off. When I say cut off I don't mean the power is cut but the boiler doesn't turn back on once the water temp gets below the threshold. I've had the oil company out over 7 times and they even out sourced to a third party oil company and they still can't figure it out.
The last oil repair person said the taco circulator wasn't on but when he removed the housing and adjusted the wires he heard it kick on. He thought that was the issue and left. It still happened after the person left later that night.
My question is would a circulator cause the boiler not to turn on when the water temp goes below the low set point? Also it is difficult to recreate because it happens randomly throughout the day.
I had a new boiler installed last year and was having random problems. During the last summer when my boiler was only being used for hot water I didn't experience any issue. As soon as fall came and we turned on the heat we started having issues again. This new issue is that the boiler randomly cuts off. When I say cut off I don't mean the power is cut but the boiler doesn't turn back on once the water temp gets below the threshold. I've had the oil company out over 7 times and they even out sourced to a third party oil company and they still can't figure it out.
The last oil repair person said the taco circulator wasn't on but when he removed the housing and adjusted the wires he heard it kick on. He thought that was the issue and left. It still happened after the person left later that night.
My question is would a circulator cause the boiler not to turn on when the water temp goes below the low set point? Also it is difficult to recreate because it happens randomly throughout the day.
0
Comments
-
-
0 -
Well we can rule out it was a licensed install with a permit and inspections. No way that flies in front of the electrical panel. And the install itself
We'd have to know a lot more by what you mean regarding 'cutting off'.
Is it running up to temperature because it's oversized and/or water is not circulating, so it shuts off the burner on high limit.
Is there enough water in the boiler and is it properly purged of air?
Is power going to the burner, but it's not running?
Is any limit open when it shouldn't be?
Despite all the people who stopped by. Doesn't seem any of them are the right one for you.There was an error rendering this rich post.
0 -
STEVEusaPA said:Well we can rule out it was a licensed install with a permit and inspections. No way that flies in front of the electrical panel. And the install itself We'd have to know a lot more by what you mean regarding 'cutting off'. Is it running up to temperature because it's oversized and/or water is not circulating, so it shuts off the burner on high limit. Is there enough water in the boiler and is it properly purged of air? Is power going to the burner, but it's not running? Is any limit open when it shouldn't be? Despite all the people who stopped by. Doesn't seem any of them are the right one for you.0
-
Very sloppy install. They blocked the electrical panel. You need 30" wide at the panel and nothing behind uou.
Anyone who installs like that will not be able to troubleshoot.
Are you having to reset the burner control? What kind of thermostat do you have? Are the batteries if any ok?
You said you had random problems after the install but that it runs ok for hot water. Is that still the case?
If it is the Hydrostat control is probably not set up properly. Open the cover and show us the settings. Read the hydrostat control so you can scroll through the settings.
Your going to have to do this if you can't find someone to fix it.
Post your location maybe someone can help.0 -
EBEBRATT-Ed said:Very sloppy install. They blocked the electrical panel. You need 30" wide at the panel and nothing behind uou. Anyone who installs like that will not be able to troubleshoot. Are you having to reset the burner control? What kind of thermostat do you have? Are the batteries if any ok? You said you had random problems after the install but that it runs ok for hot water. Is that still the case? If it is the Hydrostat control is probably not set up properly. Open the cover and show us the settings. Read the hydrostat control so you can scroll through the settings. Your going to have to do this if you can't find someone to fix it. Post your location maybe someone can help.
I have attached a picture of the hydrostat controller . When the boiler stops cutting on once the water gets below the low limit I only have to switch off and on the service switch to get things back to normal. FYI. My boiler settings are HL 180 diff 15, low limit 160 diff 10.0 -
EBEBRATT-Ed said:Very sloppy install. They blocked the electrical panel. You need 30" wide at the panel and nothing behind uou. Anyone who installs like that will not be able to troubleshoot. Are you having to reset the burner control? What kind of thermostat do you have? Are the batteries if any ok? You said you had random problems after the install but that it runs ok for hot water. Is that still the case? If it is the Hydrostat control is probably not set up properly. Open the cover and show us the settings. Read the hydrostat control so you can scroll through the settings. Your going to have to do this if you can't find someone to fix it. Post your location maybe someone can help.0
-
When there is a heat call, a green light in the bottom right corner should be illuminated.
Hi- 180
Lo- 160
Diff.- 10 on both.
You can press the button on top to scroll through the settings.0 -
HVACNUT said:When there is a heat call, a green light in the bottom right corner should be illuminated.
Hi- 180
Lo- 160
Diff.- 10 on both.
You can press the button on top to scroll through the settings.
0 -
So at 142° there is a heat call but no burner. The red light for the LWCO is not on, correct? If not, you'll need an electrical meter for the next step. Is there 120 volts across B1 and B2.0
-
I’d like to know the rest of the settings.
There was an error rendering this rich post.
0 -
HVACNUT said:So at 142° there is a heat call but no burner. The red light for the LWCO is not on, correct? If not, you'll need an electrical meter for the next step. Is there 120 volts across B1 and B2.
0 -
STEVEusaPA said:I’d like to know the rest of the settings.
0 -
HVACNUT said:So at 142° there is a heat call but no burner. The red light for the LWCO is not on, correct? If not, you'll need an electrical meter for the next step. Is there 120 volts across B1 and B2.-1
-
imxelite said:MikeAmann said:You measured at the B1 and B2 screw terminals?
If so, then it could be a bad Hydrostat. But do this first. Shut off the power. Run to the Hardware store and pick up some BX connectors (not Romex). They come in straight and angle. Somebody shouldn't be working on electric. The box is plastic and the metal plate around the bottom is for grounding. If the control isn't properly grounded, it won't function properly. And that green wire that looks like it's under the spell of a snake charmer should get connected to the green ground screw. Open the switch box and make sure its actually being used as a ground.
That's just gross.4 -
-
Thanks everyone. I have called the owner of the oil company that did the install. I am going to have them allow me to find an installer on my own to address these issues and I'll send them the bill. I really wish I knew this install was not done to code and if needed I might have to take legal action due to safety reasons.
The boiler (heat exchanger) is under a 10 year warranty but other parts are only covered for a year and I have about 3 months before that is up.0 -
imxelite said:Thanks everyone. I have called the owner of the oil company that did the install. I am going to have them allow me to find an installer on my own to address these issues and I'll send them the bill. I really wish I knew this install was not done to code and if needed I might have to take legal action due to safety reasons.
The boiler (heat exchanger) is under a 10 year warranty but other parts are only covered for a year and I have about 3 months before that is up.1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 50 Biomass
- 418 Carbon Monoxide Awareness
- 75 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 150 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 856 Plumbing
- 6.1K Radiant Heating
- 372 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 39 Industry Classes
- 47 Job Opportunities
- 15 Recall Announcements