Boiler Tripping

joe143
joe143 Member Posts: 25
Hello Folks- Wondering if anyone would know why boiler trips when oil tank goes below Half. I would need to bleed it to restart.

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • mattmia2
    mattmia2 Member Posts: 12,496
    air leak somewhere
    joe143
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 17,638
    Don't know what kind of set up you have I am assuming and indoor tank. If the oil level in the tank is above the burner pump you have gravity feed. If the oil level is below the pump you have a suction lift feed.

    With suction lift every fitting has to be absolutely airtight or it will suck in a little air and the pump will lose it's prime.
    joe143
  • CTETeach
    CTETeach Member Posts: 9
    Does the oil line come off the top of the tank? If so maybe the line isn't into the tank deep enough. So, at 1/2 at tank the line stars sucking air not oil. I've seen this quite a few times.
  • pecmsg
    pecmsg Member Posts: 5,957
    joe143 said:

    Hello Folks- Wondering if anyone would know why boiler trips when oil tank goes below Half. I would need to bleed it to restart.

    After you bleed it, it runs normally?