How to drain baseboard heating system on very old boiler (pics)
Comments
-
That actually doesn't look that terrible, on the whole... there are some things which may need replacing, but overall it looks pretty good.
Draining it shouldn't be hard. Someone gave you useful valves. Some things, like the expansion tank, may not need replacing; check how the system pressure behaves when the system heats up (once you get the air out...). That air release does look a bit sketchy. In general, though, make sure that something is actually not working before you start throwing parts at it.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
The back flow preventer has a slow leak which is prob causing all that corrosion, so I figured I’ll replace the pressure regulator along with it. The extension tank does seem to be working properly, but I can’t imagine that air bleeder above it is doing anything, and I think if I try to replace that the connection on the tank will break, it looks very corroded. I drew a sketch of the whole system, could use some ideas on how to drain it.0
-
If you are going to work on the fill system, move the expansion tank down there. Then you will be pumping away, and air problems will go away.
The air vent needs to be replaced also.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Things don't look that bad to me. I would replace the air vent on the air scoop. The air scoop is fine its just rusty from the vent leaking. You have purge and balance valves for each zone thats how you get rid of the air. Below the zone valve on the smaller zone you have a ball valve and a boiler drain. To bleed you close the ball valve put a hose on the drain valve and open it and feed water into the system. Purge till the bubbles stop , then do the other zone.
Move the expansion tank (or put a new one in) and tee it into the boiler feed water line between the feed valve and the boiler. The water feed line and the expansion tank have to be connected to each other and to the boiler on the same side of the circulator. In you case leave the circ as is and move the expansion tank You have a purge and balance valve above the boiler for the other zone0 -
Glad you guys don't think it looks too bad! I get the idea for purging the smaller zone, but how would I purge the larger zone which doesn't have a drain or shut off valve after the zone valve? If drain it at the lower valve I cant feed it water to purge. As far as moving the expansions tank, would I move the air scoop with it, or leave that where it is? Can I hang the expansion tank just passed the pressure regulator and leave the rest as is?EBEBRATT-Ed said:Things don't look that bad to me. I would replace the air vent on the air scoop. The air scoop is fine its just rusty from the vent leaking. You have purge and balance valves for each zone thats how you get rid of the air. Below the zone valve on the smaller zone you have a ball valve and a boiler drain. To bleed you close the ball valve put a hose on the drain valve and open it and feed water into the system. Purge till the bubbles stop , then do the other zone.
Move the expansion tank (or put a new one in) and tee it into the boiler feed water line between the feed valve and the boiler. The water feed line and the expansion tank have to be connected to each other and to the boiler on the same side of the circulator. In you case leave the circ as is and move the expansion tank You have a purge and balance valve above the boiler for the other zone1 -
Change out ALL of the badly corroded air-release cannisters. Air scoop is ok. Butt you you can change it out for a new Spirovent micro-bubble remover.0
-
15th picture from the top shows a drain and a purge/balence valve for the larger zone. Yes leave air scoop. Move expansion tank to make up water line between boiler and pressure reducing valve. You may have to repipe a little to get it in there. Also looks like there is an old air vent on the large zone above circ pump change that out if it doesn't work. To bleed you add water it goes down through pump through boiler out the supply pipe through the baseboard and back the return line and out the drain with the purge valve shut to keep water from coming back up the return from the boiler. Open zone valves manually with lever while bleeding0
-
As it is piped and pumped now the high air vent could actually be allowing air into the system, under some conditions, low static pressure for example
Change the expansion tank location, maybe even cap that vent off. The air purger and vents at the heat emitters should be adequate.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I was wondering about that drain and valve. There are 2 of them for each section of the larger zone, just before they combine before returning to the boiler. They are about 20+ feet from the boiler so that section wouldn't be purged, but hopefully that not a big deal. Is there any concern with purging through the boiler? Wouldn't the pressure activate the release valve? As far as replacing the old air vents and moving the expansion tank. I don't think there's a way to valve off just the tank right now, so will I need to drain the whole system to do that part?EBEBRATT-Ed said:15th picture from the top shows a drain and a purge/balence valve for the larger zone. Yes leave air scoop. Move expansion tank to make up water line between boiler and pressure reducing valve. You may have to repipe a little to get it in there. Also looks like there is an old air vent on the large zone above circ pump change that out if it doesn't work. To bleed you add water it goes down through pump through boiler out the supply pipe through the baseboard and back the return line and out the drain with the purge valve shut to keep water from coming back up the return from the boiler. Open zone valves manually with lever while bleeding
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements