Relief valve leaking
aurora22
Member Posts: 32
in Oil Heating
Ok. I have a peerless oil boiler. This also my water heater. I had a leak in the pipe at a rad the other day. Found I had no pressure. Now pipe fixed. Upon bringing the pressure to 15 lbs. when I saw too much pressure 18 lbs. I used the relief valve to remove water and pressure. Now valve leaks. Valve is old. So I’m assuming to replace. I need to know which valves to shut and how the suggested way to drain the water
0
Comments
-
Where is the relief valve? It looks like there may be isolation valves to isolate only the boiler but I can't tell from your pictures.0
-
As the water is heated the pressure will go up. 20, 22, 25#’s is not uncommon. Your safety release should be at 30#’s.0
-
Last pic. Closest to the wall. It’s immediate next to the fill valve w lever0
-
-
Last pic. Top row. Boiler feed valve , fill valve w lever and then relief valve0
-
That I at least hope is a pressure reducing valve with a fast fill lever but I can't see what it is connected to from that picture, i assume the furthest back pipe is a supply the domestic water system in to a check valve then in to the pressure reducing valve.0
-
yes I believe so. I’m not home so I’m sorry I can’t get any addl pics for a little while0
-
But yes the relief valve is what is leaking0
-
First thing to try is to snap the relief valve open and closed a few times. You may have gotten some dirt and rust in the valve seat and if you flush it it may stop leaking. It's a long shot but may work.
You need to shut the incoming valve in the water supply which is down near the floor you can see it in the 2d picture. The pipe on the relief valve outlet (heading toward the left side of the boiler) also drops down near the floor I think there is a valve there as well. Shut both those valves.
There is a union on the relief valve so you can take the pipe apart to change it. You may have to buy the relief valve and the PRV all in one package.0 -
Awesome. This is what I needed. Can u also tell me. Once replaced. Is the boiler feed line suppose to be left open?0
-
Looks like someone installed a square pressure gauge where the pressure relief valve typically goes.
You definitely don’t want a valve between the boiler and the relief valve. That could isolate the valve from the boiler and cause a serious problem
If the valve has been leaking, it needs to be replaced. Personally I would install a new one on the boiler. With a tee if you really need that gauge. Should be a gauge in the boiler jacket somewhere?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 51 Biomass
- 419 Carbon Monoxide Awareness
- 91 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 922 Plumbing
- 6.1K Radiant Heating
- 375 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 16 Recall Announcements