Ignition Control Module vs Ignitor / Cable
Comments
-
inspect the cable and inspect the electrode. If the cable is chaffed or cracked or burned it can short to ground, the porcelain in the electrode can crack and the spark can follow the crack. If it is old it wouldn't be a bad idea to just replace the cable and possibly the electrode if the electrode can be replaced without replacing the whole pilot burner.0
-
So I'm still dealing with this problem intermittently. I replaced the high voltage cable, and also got a new (used) S8600M control module. Neither really seem to have fixed the problem. Actually the new S8600M seemed to work even worse than the old one, could I have gotten a bad module? Everyone online seems to say these are super reliable. And still sometimes I knock on the module or mess with the wires and the boiler fires right up. It'll work for a few days without issues and then it'll happen again.
The electrode itself seems fine honestly, so I don't think that's it? How do I know if I have a good ground wire?0 -
You have a loose connection or a bad ground -- or both -- somewhere. May be hard to find, but check all connections and wiring.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
ironslice said:
How do I know if my steam boiler Ignition control module (Honeywell S8600M) is bad, or if it's the Ignitor/cable? The module is getting 24V but I sometimes randomly don't get a spark. The weird thing is when it happens, if I give the module a bit of a knock/tap, it'll send a spark and the boiler will fire right up.
Are you related to Arthur Fonzarelli?
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
-
Alright I'm starting to agree it's a grounding issue. I just now heard it start up twice (Main Valve fully open and boiler lit) and then immediately shut off. But I went down there and checked and there's still 26V everywhere there's supposed to be. That being said it seems like once it's running it runs reliably, this only seems to happen right at initial startup or shortly after.
Everything seems connected just fine, and I recently had a technician come here and he checked all the wiring too... I don't see any cracks on the Ignitor, where would the ground be failing a few seconds after main valve ignition?0 -
Hello @ironslice,
" new (used) " ??? You probably bought someone else's intermittent problems. They all work great until they don't. Probably poor aging solder joints in the module.ironslice said:So I'm still dealing with this problem intermittently. I replaced the high voltage cable, and also got a new (used) S8600M control module. Neither really seem to have fixed the problem. Actually the new S8600M seemed to work even worse than the old one, could I have gotten a bad module? Everyone online seems to say these are super reliable.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
Does it fail to spark or does it fail to prove flame once it lights and lock out?0
-
Two separate issues - the main one is that sometimes it will just not be on and going down and turn the power on and off doesnt restart it, until I mess with the S8600M and then it'll fire.
Second issue is that sometimes it'll start up fully, run for 10sec and then shut off (this seems to be more rare), but I was wondering if they could be related.
I ordered a new S8610M, we'll see if that helps this time.0 -
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements