Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Diagnosing a short

whydowesit
whydowesit Member Posts: 1
edited January 5 in Gas Heating
I have a client with a Rheem furnace.  The inducer fan comes on after turning the power on, (no call for heat). >>Disconnected t-stat; inducer fan motor on with power. Replaced IFC. .   Inducer on when power is switched on.
Can't figure how it's got power.
Rheem mdl#RGPH-04NAUSR

Comments

  • ratio
    ratio Member Posts: 3,805
    Check the gas valve. Some control boards will turn on the inducer for an open circuit on the gas valve.
  • 109A_5
    109A_5 Member Posts: 1,771
    Hello @whydowesit,
    Maybe also...




    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System