Diagnosing a short
Options
whydowesit
Member Posts: 1
I have a client with a Rheem furnace. The inducer fan comes on after turning the power on, (no call for heat). >>Disconnected t-stat; inducer fan motor on with power. Replaced IFC. . Inducer on when power is switched on.
Can't figure how it's got power.
Rheem mdl#RGPH-04NAUSR
Can't figure how it's got power.
Rheem mdl#RGPH-04NAUSR
0
Comments
-
Check the gas valve. Some control boards will turn on the inducer for an open circuit on the gas valve.0
-