Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Diagnosing a short
whydowesit
Member Posts: 1
I have a client with a Rheem furnace. The inducer fan comes on after turning the power on, (no call for heat). >>Disconnected t-stat; inducer fan motor on with power. Replaced IFC. . Inducer on when power is switched on.
Can't figure how it's got power.
Rheem mdl#RGPH-04NAUSR
Can't figure how it's got power.
Rheem mdl#RGPH-04NAUSR
0
Comments
-
Check the gas valve. Some control boards will turn on the inducer for an open circuit on the gas valve.0
-
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 91 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 921 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements