Replace Lux ELV4 Thermostat with Ecobee
sandman
Member Posts: 5
Is it possible to replace my Lux thermostat with an Ecobee. The Lux is line voltage on an oil heat system and i have a Taco SR-503. I just need to install the Ecobee on Zone 2.
0
Comments
-
From your pictures ALL the t-stat wiring is Low Voltage.Do you have a picture of the t-stat?0
-
sandman said:
From your pictures ALL the t-stat wiring is Low Voltage.
This is thermostat I currently have controlling both Zone 1 and Zone 2. I'm looking to just replace it on zone 2.Do you have a picture of the t-stat?0 -
A line voltage thermostat can operate a low voltage circuit, the reverse is not true.
I have a feeling that someone purchased a line voltage thermostat to do the job of a low voltage thermostat.Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
2 -
In looking over the thermostat instructions, It appears that the clock and other software and hardware in the thermostat are powered by 2 AA batteries. That would make the switching contacts able to turn a 24 volt system on and off. Although it says not to use this on a 24 volt control system in round about language, it does not specifically have a WARNING not to connect to a 24 volt system. That implies that it might work in my opinion. So you will want to be very careful to measure the voltage on the wires that the thermostat is connected to. If it is around 24 volts +,- then the Ecobee should work just fine. If it is 110V AC or 220 VAC then you can not.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
Ok, yes you can use line voltage thermostats to do 24 volt switching, especially when switching is done with an isolated 3 volts DC.
The issue is, it likely is wired using 14/2 romex or B/X. That's only 2 wires, and leaves you without a wire for a Common to 24 volt power the new thermostats.
I believe, but not positive, its against NEC to have line and low voltage wiring in the same conduit unless the wire is the same gauge, which it is not. The low volt wires are also running through the line volt section of the SR503. The relays ships with a cardboard divider to keep it separate.
And where are you getting the 24 volts to power these thermostats? Not the zone panel, right?
Since there's no option for a Common at the thermostats without running new wires, are you planning on using one of those plug in things?0 -
HVACNUT said:Ok, yes you can use line voltage thermostats to do 24 volt switching, especially when switching is done with an isolated 3 volts DC.
The issue is, it likely is wired using 14/2 romex or B/X. That's only 2 wires, and leaves you without a wire for a Common to 24 volt power the new thermostats.
I believe, but not positive, its against NEC to have line and low voltage wiring in the same conduit unless the wire is the same gauge, which it is not. The low volt wires are also running through the line volt section of the SR503. The relays ships with a cardboard divider to keep it separate.
And where are you getting the 24 volts to power these thermostats? Not the zone panel, right?
Since there's no option for a Common at the thermostats without running new wires, are you planning on using one of those plug in things?0 -
sandman said:HVACNUT said:Ok, yes you can use line voltage thermostats to do 24 volt switching, especially when switching is done with an isolated 3 volts DC.
The issue is, it likely is wired using 14/2 romex or B/X. That's only 2 wires, and leaves you without a wire for a Common to 24 volt power the new thermostats.
I believe, but not positive, its against NEC to have line and low voltage wiring in the same conduit unless the wire is the same gauge, which it is not. The low volt wires are also running through the line volt section of the SR503. The relays ships with a cardboard divider to keep it separate.
And where are you getting the 24 volts to power these thermostats? Not the zone panel, right?
Since there's no option for a Common at the thermostats without running new wires, are you planning on using one of those plug in things?HVACNUT said:Ok, yes you can use line voltage thermostats to do 24 volt switching, especially when switching is done with an isolated 3 volts DC.
The issue is, it likely is wired using 14/2 romex or B/X. That's only 2 wires, and leaves you without a wire for a Common to 24 volt power the new thermostats.
I believe, but not positive, its against NEC to have line and low voltage wiring in the same conduit unless the wire is the same gauge, which it is not. The low volt wires are also running through the line volt section of the SR503. The relays ships with a cardboard divider to keep it separate.
And where are you getting the 24 volts to power these thermostats? Not the zone panel, right?
Since there's no option for a Common at the thermostats without running new wires, are you planning on using one of those plug in things?
Ecobee might offer something you can use if there's no Common. You can also ask Taco and Ecobee about using a resistor.0 -
If our 1000ohm 1/2watt resistor doesn't work, try a P/N: 684MMR100K MFG: Cornell Dubilier / Illinois Capacitor Disc: 0.68 µF Film Capacitor 63V 100V Polyester, Metallized Radial.
There was a customer here with an issue using our Zone Sentry and Ecobee t-stat. We did some testing and the above resistor fixed his issue. Hope this helps.
1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements