Weil McClain boiler (GV-5, Series 4) "Puffs" on start

jy001
jy001 Member Posts: 12
I have a Weil McClain boiler (GV-5, Series 4) with operational issues. When it tries to start it takes an extended period of time. I have the panels off the boiler and can hear the flame "puff" 4 or 5 times before it lights.


This “puffing” is a concern since a month ago the boiler would also puff a few times, try to light and then stop. It would never start. In that scenario the troubleshooting chart, based on the fault lights on the boiler, in the manual, indicated it could be a voltage issue, ignitor or gas valve. Voltages were in spec, and I replaced the ignitor, still didn’t fire but it DID puff until it timed out


Before I ordered a gas valve, I took the entire boiler apart all the way down to the orifice that converts the natural gas unit to propane. I cleaned everything and blew out the orifice inlet with compressed air. Put it all back together and it worked for over a month without any puff until this morning when it wasn’t running. It is running now, however, with the extended puff mentioned earlier.


Just curious if this fault scenario is familiar, common, etc. Hoping to figure out the issue before it dies completely in the middle of Winter.

Comments

  • hot_rod
    hot_rod Member Posts: 23,128
    Do you have a way to check gas pressure, before and after the gas valve? You want to see static pressure, nothing running, then check pressures as the boiler fires and also at high fire.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Jamie Hall
    Jamie Hall Member Posts: 24,599
    You also need to check the draughts on the unit and make sure that the cleaning really cleaned the heat exchanger and that the breeching and flue are clear.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    SuperTech
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,161
    The trouble shooting guide has to many options to look thru without knowing some answers to what the conditions of the lights on the mater control are.
    Trouble shooting starts on page 66 of this book https://www.weil-mclain.com/sites/default/files/field-file/gv-series-4-manual_1.pdf. Observing the conditions of the control at the time of the failure, will point you in a direction to look. Without knowing answers to questions like: "are certain lights on, off, or flashing" when the sound or puffing happens we can only guess and use the parts cannon. Eventually you will find a part that will fix the problem. You may have to rebuild the entire boiler a piece at a time, but with unlimited funds, and being in no hurry you can eventually get it right.

    I would suggest using standard logical diagnosing to rule out what is not broke, until you get the the part that is broke or dirty or out of adjustment.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • JUGHNE
    JUGHNE Member Posts: 11,262
    Does the exhaust exit the lower part of the boiler?
    Did you take that apart where it connects to the CI section?

    There should be a drain tee/hose on the exhaust pipe right at the boiler, that needs to be clear.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,298
    I would check the gas pressures as others have mentioned. You need to check the gas pressures at the gas valve inlet and outlet.. Usually 12-14" wc at valve inlet and 9-11" outlet but follow what the boiler manual says

    Since you mentioned propane do you have any other propane appliances and are they working ok??

    It almost sounds like a sticking regulator. Could be the one in the gas valve, at the tank or at the inlet to the house. Chek to see if the regulator vent openings are clear. Spiders and bees like to get in there.

    Did you pull the burners out and clean them?
  • HVACNUT
    HVACNUT Member Posts: 6,242
    Check intake and exhaust and make sure both are clear.
    It's a negative pressure gas valve and should read -0.2" wc manifold.
    SuperTech
  • jy001
    jy001 Member Posts: 12
    hot_rod said:

    Do you have a way to check gas pressure, before and after the gas valve? You want to see static pressure, nothing running, then check pressures as the boiler fires and also at high fire.

    No, I dont. I will likely have to purchase a Manometer.
  • jy001
    jy001 Member Posts: 12

    You also need to check the draughts on the unit and make sure that the cleaning really cleaned the heat exchanger and that the breeching and flue are clear.

    I checked for air flow blockages when it stopped working a month ago. I have not cleaned the heat exchanger though, I'll do that the next time I take everything apart.
  • jy001
    jy001 Member Posts: 12
    JUGHNE said:

    Does the exhaust exit the lower part of the boiler?
    Did you take that apart where it connects to the CI section?

    There should be a drain tee/hose on the exhaust pipe right at the boiler, that needs to be clear.

    Are you referring to the condensate drain...??
  • jy001
    jy001 Member Posts: 12

    I would check the gas pressures as others have mentioned. You need to check the gas pressures at the gas valve inlet and outlet.. Usually 12-14" wc at valve inlet and 9-11" outlet but follow what the boiler manual says

    Since you mentioned propane do you have any other propane appliances and are they working ok??

    It almost sounds like a sticking regulator. Could be the one in the gas valve, at the tank or at the inlet to the house. Chek to see if the regulator vent openings are clear. Spiders and bees like to get in there.

    Did you pull the burners out and clean them?

    I will be purchasing a Manometer to check pressures. All my propane appliances are working fine...

    I like the idea of checking the regulator at the inlet to the house, I'll look at that today. Burners were not removed.
  • jy001
    jy001 Member Posts: 12

    The trouble shooting guide has to many options to look thru without knowing some answers to what the conditions of the lights on the mater control are.
    Trouble shooting starts on page 66 of this book https://www.weil-mclain.com/sites/default/files/field-file/gv-series-4-manual_1.pdf. Observing the conditions of the control at the time of the failure, will point you in a direction to look. Without knowing answers to questions like: "are certain lights on, off, or flashing" when the sound or puffing happens we can only guess and use the parts cannon. Eventually you will find a part that will fix the problem. You may have to rebuild the entire boiler a piece at a time, but with unlimited funds, and being in no hurry you can eventually get it right.

    I would suggest using standard logical diagnosing to rule out what is not broke, until you get the the part that is broke or dirty or out of adjustment.

    Thanks for the link, that's the same manual I have been using for months. That's how I even got to this point, running through troubleshooting, diagnostic flow charts, specifications, etc. Thats also how I came to the conclusion that the controller is functioning, the ignitor was faulty and that the gas valve was potentially faulty. All of those decisions were made based on review of the diagnostic flow charts in the manual. It is a very well written and detailed. I don't feel as though I am using a "parts cannon" at this point.

    If I had unlimited funds I would have purchased a new boiler by now.

  • JUGHNE
    JUGHNE Member Posts: 11,262
    If this is the boiler design I am thinking of, take off the front panel and find where the exhaust connects to the cast iron.
    If you look in there you may see some blockage from condensation/soot preventing smooth operation.

    A picture would help.
  • pjc_2
    pjc_2 Member Posts: 7
    Check the burner cone shown in figure 32 on page 65. These cones can develop holes over time and can cause rough ignition. We have replaced many on these gv's that had rough starts.
    jy001
  • jy001
    jy001 Member Posts: 12
    JUGHNE said:

    If this is the boiler design I am thinking of, take off the front panel and find where the exhaust connects to the cast iron.
    If you look in there you may see some blockage from condensation/soot preventing smooth operation.

    A picture would help.

    I had previously checked for blockages, etc.
  • jy001
    jy001 Member Posts: 12
    pjc_2 said:

    Check the burner cone shown in figure 32 on page 65. These cones can develop holes over time and can cause rough ignition. We have replaced many on these gv's that had rough starts.

    I should have thought of this myself, considering I already had the cone off... It was definitely worn and after having read your comment I will likely remove it again and give it a closer look.
  • jy001
    jy001 Member Posts: 12
    jy001 said:

    pjc_2 said:

    Check the burner cone shown in figure 32 on page 65. These cones can develop holes over time and can cause rough ignition. We have replaced many on these gv's that had rough starts.

    I haven't gotten to taking the boiler apart to inspect the cone, however, I did tap the gas valve with a rubber mallet this morning as it was starting/puffing. It started after a few more puffs, however, the next time there was a call for heat, it fired without any puffing and I did not tap the valve that time.... First time in weeks no puffing, quite a coincidence considering I had just tapped the valve the previous fire. What is your opinion on the issue potentially being a sticky valve...? Just curious... Thanks...