Vent Size for 1 pipe Steam House
bdc_diy
Member Posts: 8
Hello,
New to this. New boiler, all radiator vents >20 years old. Replaced two Dole 3C main vents (completely plugged) with Gorton #1. Attached is a simple power point with the piping. There are three upstairs radiators. Downstairs heats fine. Upstairs is the problem, the middle heats fast, almost inline with the main boiler. The other two are slow to heat. One very very slow.
Was the Gorton #1 a good choice? Should I get a larger vent?
Learned about this as there was no advice or information on uneven heat from installer. Started search around and found both Silent Steam and Garry Gill youtube.
Thanks
bruce
New to this. New boiler, all radiator vents >20 years old. Replaced two Dole 3C main vents (completely plugged) with Gorton #1. Attached is a simple power point with the piping. There are three upstairs radiators. Downstairs heats fine. Upstairs is the problem, the middle heats fast, almost inline with the main boiler. The other two are slow to heat. One very very slow.
Was the Gorton #1 a good choice? Should I get a larger vent?
Learned about this as there was no advice or information on uneven heat from installer. Started search around and found both Silent Steam and Garry Gill youtube.
Thanks
bruce
0
Comments
-
You can't go too large on main vents . You don't want any resistance on the main vents . You want the main to charge first .. You need resistance on the radiators vents to direct the steam down the main first and then to the radiators
First size the vents to the size of the radiator and increase size if needed. Work your way up slowly .It is best to have an adjustable radiator valve or different size caps ......There was an error rendering this rich post.
0 -
@bdc_diy , how long are your steam mains, and what pipe size?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
I tried to add a power point hope it will work. It shows the up. Thanks for all remarks.
0 -
All the runs to all the radiators are 1.5" OD pipe.
0 -
That's 1-1/4" I.D.bdc_diy said:All the runs to all the radiators are 1.5" OD pipe.
The pipe coming off the boiler would be 2-1/2". What about the two pipes after the split- what diameter are those?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
After the split they are 2" OD. 1.5" OD going upstairs, 15' up. That radiator gets hot quickly. Almost inline with the main pipe.0
-
That's where your steam is going first. Try slowing that one down a little
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
So each of the main lines that feed groups of radiators, one going front and one going back, are 2" O.D>? That's kind of unusual, except in very small houses.........bdc_diy said:After the split they are 2" OD. 1.5" OD going upstairs, 15' up. That radiator gets hot quickly. Almost inline with the main pipe.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
I will have to get under the insulation and check.0
-
Thanks for you help and patients. I new to this. Many updates. Found a chart to convert OD to ID so now all the pipe diameters ID's are listed. Starts at 2.5" out of the boiler. Split is 2". The front loop stays 2" till the return. There 1.25". The back loop, 2" -> 1.5" -> 1.25" progressively. Updated power point attached.
All the radiator feeds including the verticals to the 2nd floor are 1.25 ID.
Thanks!0 -
So I took the numbers in the power point and calculated the volumes in the two loops. I split the volume in the main pipe between the front loop and the rear loop.
1.0 CF Front loop
1.1 CF Rear loop
Is a Gorton #1 appropriate for a main vent for that volume?
0 -
Yes. if not, add more
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Key resources:
Youtube:
HeatingHelp
silentsteam
Sites:
https://www.gwgillplumbingandheating.com/ Garry Gill's website
HeatHelp.com
Searching this site heatinghelp.com using many different key words.
Watched many of the detailed and helpful youtube videos.
What I did:
There are 2 main loops.
First bought 2x Gorton #1, one on each loop. Too little venting (an opinion on my part).
Bought and added 2x Gorton #2. One each on each loop (size difference dramatic).
8 radiators in house, bought 8x Vent Rite Adjustable vents.
Main vents installed. #2 and #1 on each loop though #1 will not add much.
In the process of installing new radiator vents. Not doing all at once.
Thanks for those that stopped by and to those for maintaining this site!
0 -
So, @bdc_diy , how does it work?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements