Was this a vapor system?

SethYank
SethYank Member Posts: 36
I am quoting a new steam boiler for a small house in town. there are 7 radiators, approximately 187 square feet or radiation. There are no traps any where in the system. There are dry returns to the existing boiler, the dry returns meet under the only vent in the system, this line drops down and goes into the bottom of the boiler. The wet returns join up and enter the back bottom of the boiler, no hartford loop. Currently there is a leaking 250 mbh smith boiler there, with the top outlet piped directly into the steam main, no equalizer or any thing. The radiators have a top entering adjustable handle valve with a bottom exit, no trap.
I am flipping through the lost art trying to see how I should bring all these returns to the boiler, and looking at the install manual to figure out my risers and header in the space allotted. Help is appreciated.

Comments

  • SethYank
    SethYank Member Posts: 36
    here are a couple of pictures


  • SethYank
    SethYank Member Posts: 36

  • Jamie Hall
    Jamie Hall Member Posts: 24,584
    That is indeed a vapour system. The valves are adjustable to allow just enough steam in to match the size of the radiator -- provided the pressure is kept low. Further, don't assume that the return elbow is just an elbow -- many vapour systems had one of a variety of patented designs to keep steam in the radiator, but allow water and air out. Again, however, provided the pressure is kept low.

    Joining the dry returns at the boiler with a vent is correct. There should also, however, be some arrangement -- most commonly a steam trap -- at the end of each main to let air into the dry returns but keep steam out, and if the system is parallel flow (most were) there must also be a drip from both the steam main and the dry return to the wet return at that location.

    The near boiler piping should be what the manual for the boiler requires, or better. Keep the single vent at the top of the dry returns before dropping. It is best, if using a drop header, for the various mains to connect with the header individually, however, rather than having a single riser and Ts at the top.

    Now back to pressure. The new boiler MUST have a vapoustat with a 0 to 16 ounce range. For initial testing, try having the cutout at 8 ounces with a differential (subtractive) of 4 ounces, giving a cutin of 4 ounces. Best practice also requires a low pressure gauge in addition to the required 0 to 30 psi gauge; 0 to 3 psi is most common, but 0 to 5 is satisfactory. This is used to verify that the vapourstat settings are correct -- they have been known to be out of calibration.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    mattmia2
  • Steamhead
    Steamhead Member Posts: 17,330
    @SethYank , that is some sort of Vapor system. Can you post a pic of the writing on the top of the valve? Also, what is at the radiator return connections? Post a pic of that too.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • mattmia2
    mattmia2 Member Posts: 10,771
    It still is a vapor system, you need to set the new boiler up as such if you want it to work right. Make sure you don't oversize the boiler, maybe even work in the pickup factor as 10% or so or calculate the piping instead of using the 30% baked in to the rating plate. Set it up with a vaportstat.
  • SethYank
    SethYank Member Posts: 36
    I was using 1.5 for my pick up factor, I saw where Dan had recommended that. The risers to the second floor (4 radiators) are all un insulated.
    The radiator in the kitchen is not original, I think it is bigger than original by a few sections, but it is not really working. They used a regular valve at the bottom like a one pipe system, with an air vent at the top of the same section. This radiator is at the end of the back main header. The home owner says it doesnt really heat but they dont need heat in the kitchen. There are financial difficulties and since they dont need the heat I thought I would address this later. The opposite end of the radiator is plugged at the bottom, so is the return line. Picture attached.

  • Steamhead
    Steamhead Member Posts: 17,330
    edited December 2023
    With the vent on the same section as the valve, only that section will heat.

    What is on the outlet connection of the original radiators?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • 109A_5
    109A_5 Member Posts: 1,478
    Hello @SethYank,
    Wow that boiler seems HUGE for that application.

    Even one of these is too big.




    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • SethYank
    SethYank Member Posts: 36
    I did not get a picture of the top of the vent, attached is a picture of the radiator outlet.
    there is no trap at the end of the mains and does not look like there ever was. The end of the mains angle down and return to the boiler below the water line. The dry returns come into a cross with the vent on top and the bottom drops straight down and into the bottom of the boiler. I am thinking the dry return should be tying into the wet return and returning to the boiler through the hartford loop, correct? I was planning on getting a vapor stat.
    I am planning on using a Utica UH1604HSID, four section boiler, the iom says to use a single 2 1/2" riser, the 5 sections call for 2 risers. I was wondering if using two 2" risers into the header would work, I know I am downsizing the riser and should not but doubling the riser should slow the steam down
  • SethYank
    SethYank Member Posts: 36


  • SethYank
    SethYank Member Posts: 36
    The house was built in 1927, the old rake and poker are still in the corner, so I think this was originally coal fired.
  • Steamhead
    Steamhead Member Posts: 17,330
    @SethYank that looks like a standard return elbow. Unless we're missing something, this is an Orifice Vapor system. The orifice is located in the radiator shutoff valve, and is sized to keep the radiator from filling more than 85% or so at a certain boiler pressure. In this way, steam cannot reach the dry returns.

    AFAIK, MEPCO still makes orificing valves. Or, you can get orifice plates from Tunstall, drill them to the proper size and add them to standard valves.

    On this system, the pressure control should be a Vaporstat that cannot be set higher than 1 PSI. The standard Pressuretrol cannot be set low enough for this system to work well.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    mattmia2
  • mattmia2
    mattmia2 Member Posts: 10,771
    the way it is now the mains vent through the radiators and through the returns. I think that works as long as the vent on the returns is big but others know better about that than i do.

    the closer the boiler size is to the connected edr, the less work the vaporstat has to do. 50% pickup factor is even worse than 30%. unless there is a ton of piping it is far less than even 30%.
  • 109A_5
    109A_5 Member Posts: 1,478
    Hello @SethYank,
    I think the Boiler Sq. Ft. needs to match the EDR.



    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • SethYank
    SethYank Member Posts: 36
    So I should step back to the 1603, I just get worried because years ago I undersized a boiler and it created all kinds of problems.
  • SethYank
    SethYank Member Posts: 36
    I presumed the air is venting through the radiator back to the central vent at the radiator, I am not sure if there are orifice plates somewhere around the radiator.
  • SethYank
    SethYank Member Posts: 36
    Should the dry return drop be coming in before the hartford loop.
  • Steamhead
    Steamhead Member Posts: 17,330
    SethYank said:

    Should the dry return drop be coming in before the hartford loop.

    Yes.
    SethYank said:

    I presumed the air is venting through the radiator back to the central vent at the radiator, I am not sure if there are orifice plates somewhere around the radiator.

    The orifice is likely built into the valve. It might be some sort of adjustable shutter or similar device, but in general is not a separate piece. It would help if we could see what's on top of that valve.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Jamie Hall
    Jamie Hall Member Posts: 24,584
    Well... try it without adding main vents. However, if the pressure behaviour of the boiler says you need them, which it may, the system will work better (faster) if you can figure out how to add them. Some old systems didn't have either main vents or crossover traps, as a coal fire doesn't heat fast enough to really make that much difference.

    There is, from your description, nothing much wrong with the dry return except, as you note, it probably should hook into the wet return before the Hartford Loop.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • 109A_5
    109A_5 Member Posts: 1,478
    Hello @SethYank,
    SethYank said:

    So I should step back to the 1603, I just get worried because years ago I undersized a boiler and it created all kinds of problems.

    Basically, yes. However I would double check the EDR calculations (any hidden radiators). My 9 radiators are 347 EDR and even if I remove the two biggest ones from the calculations I have more EDR than 187, and my radiators are not that big. My boiler is the rare undersized one at 300 Sq. Ft. and even at 0 degrees Fahrenheit outside it only runs at about 60% duty cycle. My system never goes above 1.25 WC or 0.722 Ounces of pressure.

    With your case the other thing is the existing boiler is so big, does the system have other issues that it does not heat the building correctly ? Was it down fired ? The old boiler must have been short cycling on pressure miserably or the structure's heat loss may be incredible.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • SethYank
    SethYank Member Posts: 36
    The supply piping to the first floor radiators is very short and insulated in the basement, 3 radiators.
    The supply piping to the 2nd floor ( 4 radiators) is about 8 feet tall each and uninsulated.
    Most of the radators are thin tube, 5 tube. The bathroom is a column type and so is the kitchen.
    LR 5 tube 13 section 8 1/2" x 25" 3 1/2 edr each 45.5 total
    DR 5 tube 7 section 8 1/2" x 25" 3 1/2 edr each 24.5 total
    kit 3 tube 14 section 9" x 25" 3 3/4 edr each 52.5 total I undersized this one
    bath 3 tube 4 section 5" x 35" 2 edr each 8 total I over sized this one
    back br 5 tube 6 section 8 1/2" x 36" 5 edr each 30 total
    mid br 5 tube 4 section 8 1/2" x 36" 5 edr each 20 total
    frt br 5 tube 12 section 8 1/2" x 22" 3 edr each 36 total
    216 1/2 edr total
    The kitchen radiator is a replacement wider than the original, I can see the original riser hole.
    They also brought the steam in the bottom right side like a one pipe system, and put the air vent at the top of the same section as the inlet, so it has never heated well ( the owner has lived there 20 years) but he has no complaints of the kitchen being cold. I plan to address this with him later. But how much edr do I want to assign to this radiator. The 216 1/2 is more than the 195 edr for the 1603 But do I need more?
    I will go back to look at the vent top, I expect it is the original from the coal fired boiler, which means it should lock shut to hold a vacuum, so I should probably replace it.
    I appreciate every ones help, I am trying to fix this system since the last install was an abortion.
  • reggi
    reggi Member Posts: 523
    Yes, that one pipe wouldn't of worked nicely with the vacuum system at all... That would of upset the entire system??? Single Vent/Vacuum trap and the one pipe radiator?? Right ?
    One way to get familiar something you know nothing about is to ask a really smart person a really stupid question
  • 109A_5
    109A_5 Member Posts: 1,478
    Hello @SethYank,
    I would use the actual EDR of the actual radiators, since that is what is there and defective venting or piping could be repaired with the new boiler install or after. As far as the kitchen radiator, if someone increased the size of that radiator at some point there was an issue, whether they fixed the issue or not maybe forever unknown.

    I don't know if there is a rule of thumb to go to the next size up or down when the EDR fall between available boiler choices, and if a "Vapor" system actually makes a difference. Maybe a slight bias in size if in North Carolina versus Northern Minnesota, since the design day temperature may be different.


    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • Steamhead
    Steamhead Member Posts: 17,330
    @SethYank , use the 1604.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • mattmia2
    mattmia2 Member Posts: 10,771
    the kitchen radiator was probably replaced to get more space.
  • reggi
    reggi Member Posts: 523
    Steamhead said:
    @SethYank , that is some sort of Vapor system. Can you post a pic of the writing on the top of the valve? Also, what is at the radiator return connections? Post a pic of that too.
    That's beefier than the Kriebel but that return outlet probably has a surprise inside .
    One way to get familiar something you know nothing about is to ask a really smart person a really stupid question
  • SethYank
    SethYank Member Posts: 36
    The writing on top of the vent is "Jas P Marsh chicago, thermodisk #5"