PVC or CPVC for a low (below the waterline) return?
bruce_21
Member Posts: 241
Comments
-
Probably, for a while.bruce_21 said:My client's steel low return is clogged and rotted, likely because its partly buried in the dirt floor of the basement. Will PVC or CPVC pipe work here?
But I wouldn't do it. PVC's glass transition temperature is around 176F. Meaning, it becomes soft.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Use copperBr. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
No way..Copper is the way to go but make sure you have atleast 3/4" boiler drains on either end. I like gate valves just above them so you can always power-flush them in the future...Mad Dog 🐕0
-
-
This is the Mad Dog 🐕 Method. I PREFER gate valves because they are full port AND The Teflon Ring in a Ball Valve does not hold up well over time with 210 plus Temps, but I have used them in a pinch...Mad Dog 🐕0
-
The issue I've seen with the PTFE ring isn't from heat but seemed to be from debris chewing it up. I had a beautiful 1.5" ball valve on the skim port that even the nice plating on the ball was destroyed.Mad Dog_2 said:This is the Mad Dog 🐕 Method. I PREFER gate valves because they are full port AND The Teflon Ring in a Ball Valve does not hold up well over time with 210 plus Temps, but I have used them in a pinch...Mad Dog 🐕
My original boiler drains were also ball valves. All of them, or almost all have been replaced. For boiler drains I went back to good old washer type valves and the skim port I just used a brass plug.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment1 -
-
Plastic pipe won't be able to handle the 180f+ heat of steam condensate. Copper ($) or brass pipes ($$$) below the water line is fine. If you use copper, there must be appropriate galvanic isolation of copper from cast iron (use brass/bronze valves or fittings to avoid connecting copper directly to iron)bruce_21 said:My client's steel low return is clogged and rotted, likely because its partly buried in the dirt floor of the basement. Will PVC or CPVC pipe work here?
0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements