wood boiler aquastat what do i need?
fryfour
Member Posts: 4
hi
im trying to figure out what type of aquastat i need to run a circulator pump on a wood boiler. i want the pump to come on at say 160 and stay on no matter how hot boiler gets. the one i have can do that buts cuts off when it gets hotter . is there one made that doesnt have a differential? thanks
What model aquastat do you have? Some of them have three terminals, and can be used to make on rise (what you want), or make on fall.
An L4006B will do what you want, most of them have an adjustable differential.
i have a l4006b. It doest have the adjustable differential dial? i think its fixed .. so if i have it power the pump at 160 will it stay powered on until the water temp drops back to below 160 or does the differential cause it to loose power if it goes higher than the differntial?0
Can we back up a bit here?
What brand of wood boiler do you have and what model?
Do you have a triple aquastat to control the boiler to begin with?
You need to download the installation manual for your L4006B before you do anything.0 -
I hope you have some sort of emergency dump zone for that boiler which will work even without electrical power...Br. Jamie, osb
I forgot about that "Incident" jesmed1 it was down right ugly.0
its a mascot wood boiler.. i dont have a triple aquastat..... this is not going through any thermostat ...it will heat when i build a fire. all i want is circulating pump to come on at set temp and go off at when it gets bellow that temp and yes it has saftey blow off valve on top of boiler0
@fryfour
You need a reverse acting aqustat (one that makes contact on a temperature rise) L4006b1165 will do it if you want an imersion aqustat. If you want one that straps on the pipe those are available as well0 -
thanks Ed... that sounds good , i can set it to come on at 160 degrees and it will stay on up to 200 degrees and not shut off utill boiler temp goes back down below 160 degrees ? correct0
is the boiler outside? What about freeze protection?
Id use an electronic setpoint control, much more adjustment and they are both NO and NC
Make or break on temperature rise, by selecting heating or cooling
Ranco, Johnson Controls, Honeywell, etcBob "hot rod" Rohr
Living the hydronic dream0 -
A temperature and pressure safety valve is a necessity, yes. However, in my professional opinion it is not adequate for a solid fuel fired boiler, as it will not protect the boiler in the case of an excessive fire -- which will happen, sooner or later. Unless the boiler is to be attended at all times, and has a positive way to shut off the draught to the fire, it must have a dump zone capable of absorbing all the energy from a full load of fuel -- how big that is depends on the boiler fire box -- and that dump zone must be set up so that the boiler can thermosiphon into it without depending on pumps.Br. Jamie, osb