Another New A2W HP

Comments

  • Hot_water_fan
    Hot_water_fan Member Posts: 2,015
    The Caleffi dual fuel webinar today mentioned some new offerings too!
    JakeCK
  • hot_rod
    hot_rod Member Posts: 22,827
    There may be some limitations as to bringing LP refrigerant systems in to the U.S. ?
    Sometimes they get into Canada easier, you may already see LP units in Canada if you look deep.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,102
    R290 (propane) is already here and is used in food service refrigeration. I know True is using it. No different from other refrigerants except it is obviously flammable but the service procedures are not much different. Evacuating and charging are basically the same. The whole charge needs to be removed and purged with nitrogen to do and refrigerant repairs or brazing could be exiting if the procedures are not followed
    ChrisJpecmsg
  • fentonc
    fentonc Member Posts: 264
    There are starting to be some interesting 'high-temperature' A2W heat pumps that are at least theoretically available in the US:

    https://www.mbtek.com/collections/air-to-water/products/apollo-heat-pump-max-heat-36k-btu-3-ton-air-to-water-evi-inverter-dc-technology

    and:

    https://www.arcticheatpumps.com/high-temperature-heat-pump.html

    These really are designed to be drop-in replacements for boiler retrofits - the MBTek unit advertises a COP of 2.0 with 167F SWT and an outdoor temp of 10.4F.
  • pecmsg
    pecmsg Member Posts: 5,114

    R290 (propane) is already here and is used in food service refrigeration. I know True is using it. No different from other refrigerants except it is obviously flammable but the service procedures are not much different. Evacuating and charging are basically the same. The whole charge needs to be removed and purged with nitrogen to do and refrigerant repairs or brazing could be exiting if the procedures are not followed

    The only difference is those Systems are limited to 6 or 7 Oz total charge of R-290. 1 workaround is having 2 complete and independent Systems in the same cabinet.
    GGrossWMno57