Boiler stopped working
Frankbig23
Member Posts: 5
I have a crown gas spark fired steam boiler. Was installed maybe 3 years ago. Got home from work and it wasnt on. Jumped the thermostat didnt kick on. I cleaned the low water probe it wasnt really dirty. I took the pressurtrol off and blew out the pig tail then i jumped the trol still nothing. Damper is open and every 15 mins i see the led come on for the cycle guard lwco intermittent test. Im thinking there must be an electric issue any advice on where to start?
0
Comments
-
Check the draft hood spill switch or flame roll out. Most likely the spill switch as you stated the damper is open so those two devices would be in series after the damper end switch. Hard to believe you would have a plugged HX after 2-1/2 years so i'm leaning towards the spill switch. If the spill switch has failed you need to find the cause. It's a safety device. You might have animals nesting on top of your chimney, dead birds at the base, etc. spill switch should be re-settable by pressing the button in the middle0
-
Any lights on the Crown control board?0
-
pedmec said:Check the draft hood spill switch or flame roll out. Most likely the spill switch as you stated the damper is open so those two devices would be in series after the damper end switch. Hard to believe you would have a plugged HX after 2-1/2 years so i'm leaning towards the spill switch. If the spill switch has failed you need to find the cause. It's a safety device. You might have animals nesting on top of your chimney, dead birds at the base, etc. spill switch should be re-settable by pressing the button in the middle0
-
WMno57 said:Any lights on the Crown control board?0
-
I had to go to work when im home ill get pictures0
-
This looks to be the same set up i have CROWN BOILERCrown Boiler BSI172ENP 172 MBH Gas-Fired Fully Assembled Steam Boiler0
-
Hello @Frankbig23,
Probably something in the Yellow boxes. A Multi-meter would help.
Damper End Switch.
FRS - Flame Roll Out Switch.
BVS - Blocked Vent Switch.
Ignition Module.
https://www.velocityboilerworks.com/documents/bermuda_installation_manual_2012.pdf
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements