Air source heat pump vs oil boiler with tankless
I live in the Northeast, Connecticut in particular.
I have air source heat pump and oil fired boiler with tankless hot water.
Comments
-
What type of control is on the boiler?
And do you need to have hot water during the day? Or is everyone at work?0 -
On paper it is worth running HP when outdoor temps are mild. However, you have a valid point. If boiler is all hot anyway why not use it instead of putting hours on the HP. Add a HP water heater to the mix then you don't start boiler till it is cold. You didn't say how the oil heats your house. HP is a great combo with floor heat for those not so cold seasons, enabling a little quick heat without pumping a lot of heat in floor just to overshoot in the afternoon.0
-
Sorry the boiler feeds, baseboard heaters. House built 02’ so fairly well insulated etc.
i have Honeywell for control at the boiler, yes need hot water during day.0 -
Aquastat controller*0
-
Even if the boiler stays hot for the tankless coil, if you are not circulating water out of it, the oil consumption is only what is required to keep the boiler itself warm
If you calculated the operating cost of both systems, then you would have a better answer.
Some suggest the HP down until the COP drops below 1, or a low ambient temperature lockout prevents it from runningBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
hot_rod said:Even if the boiler stays hot for the tankless coil, if you are not circulating water out of it, the oil consumption is only what is required to keep the boiler itself warm If you calculated the operating cost of both systems, then you would have a better answer. Some suggest the HP down until the COP drops below 1, or a low ambient temperature lockout prevents it from running0
-
It depends on how old the HP is, what type of refrigerant. New models claim to work below 0 degrees. Your manual may have some performance data? My issue was the cold air temperature that they blow out in cold outside conditions.
If you are at work during the day or get passive gain, that may be comfortable enough for you?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Mitsubishi h2i they claim -13°. Installed last March so first heating season with it, I do have a smart oil gauge and energy meter for the HP just trying to play around with both and find the most efficient combination. I have noticed the cold air you mention as the fan constantly runs at a low speed when not heating. Also sometimes will get a cold flow if the unit is in defrost.0
-
What's your cost per Kwh?To learn more about this professional, click here to visit their ad in Find A Contractor.0
-
Mitsubishi h2i they claim -13°. Installed last March so first heating season with it, I do have a smart oil gauge and energy meter for the HP just trying to play around with both and find the most efficient combination. I have noticed the cold air you mention as the fan constantly runs at a low speed when not heating. Also sometimes will get a cold flow if the unit is in defrost.Constant blower is a setting, you can turn it off. At todays oil prices, run that heat pump!0
-
Robert O'Brien said:What's your cost per Kwh?0
-
Hot_water_fan said:Mitsubishi h2i they claim -13°. Installed last March so first heating season with it, I do have a smart oil gauge and energy meter for the HP just trying to play around with both and find the most efficient combination. I have noticed the cold air you mention as the fan constantly runs at a low speed when not heating. Also sometimes will get a cold flow if the unit is in defrost.Constant blower is a setting, you can turn it off. At today’s oil prices, run that heat pump!0
-
Ah... maybe not in Connecticut, @Hot_water_fan . The lowest price for residential electricity in CT at the moment is $.31 per KWh, and scheduled to go up about 10% in January. That works out to just under a dime for resistance, or perhaps 4 cents for a heat pump in colder weather, per mBTU. The OP should be able to get oil at less than 3 cents per mBTU -- I'm paying 2.4 this winter. Even with an 80% boiler, the oil is going to be cheaper.
That said, using a heat pump for spot heating does make sense -- the house Cedric powers has an apartment in it, and the tenant likes it a good bit warmer, so there is a heat pump for that space -- so Cedric does the heavy lifting, and the heat pump keeps the tenant more or less happy.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
@Jamie Hall that’s not what OP said. Anyway, let’s use $/MMbtu only for comparisons. Easier to comprehend.0
-
-
Jamie Hall said:Ah... maybe not in Connecticut, @Hot_water_fan . The lowest price for residential electricity in CT at the moment is $.31 per KWh, and scheduled to go up about 10% in January. That works out to just under a dime for resistance, or perhaps 4 cents for a heat pump in colder weather, per mBTU. The OP should be able to get oil at less than 3 cents per mBTU -- I'm paying 2.4 this winter. Even with an 80% boiler, the oil is going to be cheaper. That said, using a heat pump for spot heating does make sense -- the house Cedric powers has an apartment in it, and the tenant likes it a good bit warmer, so there is a heat pump for that space -- so Cedric does the heavy lifting, and the heat pump keeps the tenant more or less happy.I’m not positive how to do the math maybe someone smarter than me could post the numbers per btu0
-
Well, one kilowatt hour -- KWh -- is 3,400 BTU. One gallon of oil is about 140,000 BTU. So if your electric rate is currently $.255 per KWh, that is $0.075 per thousand BTU. If your oil is $3.25 per gallon, like mine, that is $0.023 per thousand BTU.
However, those are raw figures. For electric resistance heating those are also net figures for your heat, since electric resistance heating turns all of the energy directly into heat. For a heat pump, however, there is the "COP". Heat pumps have a somewhat magical air about them, but the bottom line is that through soem thermodynamic wizardry they extract heat from the outside air (usually) and raise its temperature, so it can heat the house -- and thus they use less electricity to provide heat than direct would. The COP is quite variable, but a reasonable figure to use in cold weather would be 2.5 -- that is, they deliver about two and a half times as much heat as they take electricity to run. Another way of looking at it is that the cost of a BTU delivered is the cost of the electricity divided by the COP -- in this particular case, then, your 0.075 divided by 2.5, or $0.03. On the other hand, not all of the heat in the fuel oil winds up heating your house -- so again we divide, in this case the cost of a BTU or oil by the efficiency of the boiler, which in your case is your $0.023 divided by 0.85, which comes out to $0.027.
Close to a wash.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
If my math is correct,
1M/btu oil 139,400/3.69 85% = $32.11
1M/bto HP 1M/3412x.255/2= $37.760 -
-
-
I have thought about indirect although, both plumbers I spoke with said I could run into bigger problems with boiler leaking. Since the boiler has never really “cooled down” if I switched I could end up with leaking.0
-
mike3181 said:I have thought about indirect although, both plumbers I spoke with said I could run into bigger problems with boiler leaking. Since the boiler has never really “cooled down” if I switched I could end up with leaking.1
-
HVACNUT said:mike3181 said:I have thought about indirect although, both plumbers I spoke with said I could run into bigger problems with boiler leaking. Since the boiler has never really “cooled down” if I switched I could end up with leaking.
Not sure maybe they were just not interested in doing the work, talking me out of it?0 -
If my math is correct,1M/btu oil 139,400/3.69 85% = $32.11
1M/bto HP 1M/3412x.255/2= $37.76@mike3181 I have a Mitsubishi hyper heat as well, and get around 2.8 COP when I compare kWh to the therms I used to buy, so I think 2 is selling the system short.
Your strategy is well thought out - the average day’s low temperature is regularly between 4 and 6 AM, so this is when the heat pump COP would be lowest and also when the boiler run time would be highest (best for boiler efficiency). A lot of attention is paid to “shoulder seasons” but with how much variability happens day to day, “shoulder hours” probably makes more sense to be frank.
0 -
mike3181 said:HVACNUT said:mike3181 said:I have thought about indirect although, both plumbers I spoke with said I could run into bigger problems with boiler leaking. Since the boiler has never really “cooled down” if I switched I could end up with leaking.
Not sure maybe they were just not interested in doing the work, talking me out of it?
An indirect with a modern, boiler reset aquastat will save you $$.2 -
Hot_water_fan said:If my math is correct,1M/btu oil 139,400/3.69 85% = $32.11
1M/bto HP 1M/3412x.255/2= $37.76@mike3181 I have a Mitsubishi hyper heat as well, and get around 2.8 COP when I compare kWh to the therms I used to buy, so I think 2 is selling the system short.
Your strategy is well thought out - the average day’s low temperature is regularly between 4 and 6 AM, so this is when the heat pump COP would be lowest and also when the boiler run time would be highest (best for boiler efficiency). A lot of attention is paid to “shoulder seasons” but with how much variability happens day to day, “shoulder hours” probably makes more sense to be frank.
so my break even point being my electric rate is on the higher side is low to mid 30°s0 -
HVACNUT said:mike3181 said:HVACNUT said:mike3181 said:I have thought about indirect although, both plumbers I spoke with said I could run into bigger problems with boiler leaking. Since the boiler has never really “cooled down” if I switched I could end up with leaking.
Not sure maybe they were just not interested in doing the work, talking me out of it?
An indirect with a modern, boiler reset aquastat will save you $$.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 912 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements