Steam Boiler Vaporstat Help
I replaced my pressuretrol with a vaporstat, and I am have some trouble with the settings. I started with the main at 8 oz/in2 and the cut in at 4 oz/in3. It ran fine for a couple weeks but then the boiler wouldn't turn on. As soon as i raised the main to 12 oz/in2, the boiler kicked on and has been running. I have a oz pressure gauge installed and it runs all the way up to the 16oz/in2 then turns off as expected. Any help or advice to get this set correctly? I was originally told i dont want to be above 8 on the main.
Most my radiators are running the trane vapor system.
I have 3 gorton #2s on the main and 1 on the air accumulator.
The house is being heated well. I am just worried about cycling on the boiler and getting it set correctly.
    Jamie Hall Member Posts: 27,308
    Double check that that pigtail is really and truly open all the way into the boiler. The boiler not turning back on strongly suggests that there may be a problem with that.
  • Cyclone33
    Cyclone33 Member Posts: 34
    Is it possible to snake that pigtail? I am a little leery to try to take it out. Looks like its been there awhile.
    Try a VERY long zip tie -- and blow and pour water through it.
  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,538
    I personally put my Pressuretrols & Vaporstat much higher than that. The reason is you may not be getting the most accurate reading so close to the boiler eater line. Ill put up a Picture of how I like em..Mad Dog 🐕
  • Mad Dog_2
    I have found in both Low Pressure Steam and Vapor applications, this really help you dial in the sweet spot..and that will take time...Mad Dog 🐕
  • Cyclone33
    @Mad Dog_2 Thanks! Just to help understand. Should i raise it higher or move it out away also?