Main venting
TwoTones
Member Posts: 52
Have a small one pipe steam system, had the main vent changed a year ago. Vent functions as I can hear it pushing air out of the main and closing when full of steam. I have been fine balancing the system and fixing small leaks. System is functioning well, however I noticed the plumber put a cheapo maid o mist type main vent.
Should I bother changing to a Gorton #2 to possibly get better reliability and performance or should I leave the vent? Sometimes when it isn’t broken you shouldn’t fix it…
1
Comments
-
Gorton are the Gold Standard, Hoffman are well made too..The rest?? Ehh. Swap it out do u have the Height? You could always make a mini battery of Gorton #1s...Much Shorter. Mad Dog 🐕0
-
How long is the main, and what pipe size? What model Maid-o-Mist is there now?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
It’s a 2.5 inch insulated main that runs 32 feet and I have a picture of the box
0 -
Vent is at the end of main. Plenty of clearance for something tall0
-
Yeah, that one's too small. Put on a Gorton #2, with a 3/4"x1/2" bushing so it will fit the 3/4" hole where the M-o-M is now.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Stick with Gorton's over no name vents, you will be much better off in the long term.0
-
that's not a Maid O Mist
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
Who knows who makes it. A search leads you to "World & Main, LLC
@TwoTones
If this main is heating fast I wouldn't change it but when it needs changing use a Gorton1 -
I might stick with vent until it dies and replace with Gorton 1 because I have heat arriving at every radiator/convector on two floors at almost the exact same time.
I know venting the main as fast as possible is always recommended, but if I add a Gorton 2 with a bushing, is there a chance I throw the system off balance? When I bought the house it had a Hoffman main vent which was stuck open. Believe that vent is one of the slowest…1 -
Just return it...Why put something in with a minimal life? A Gorton #2 will expel much more air meaning less fuel burned. Spitting vents can scald someone and do water damage! ⚠️ ⚠️ ⚠️. Mad Dog0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements