My boiler pressure is about 25 psi just a little bit below 30
Linotapia
Member Posts: 6
in Oil Heating
My expansion tank was bad which I decided to change it and also change the water feeder reducer valve and now the pressure a little bit higher. I’m not seeing water from the relief valve but I’m just worried about it.
what can I do ?
what can I do ?
0
Comments
-
It's possible that the tridicator gauge is no good... or the feed valve is turned up too high.....or there could be air in the system.....
Is this pressure constant, or only when up to temperature?0 -
The expansion tanks air pressure needs to be set before installing the tank. The fill valve pressure also needs to be set after installation and confirmed with a good working pressure gauge, not the one on the boiler. You can't just take these parts out of the box and install them.0
-
So now that’s mounted. Can I still fix it like adjusting both units expansion tank and the feeder valve or how can I test it if it’s the correct pressure?0
-
By the way, the pressure is constant.0
-
The only way to adjust -- or even reliably check -- the expansion tank's precharge pressure is to have it isolated from the system and completely empty of water.Linotapia said:So now that’s mounted. Can I still fix it like adjusting both units expansion tank and the feeder valve or how can I test it if it’s the correct pressure?
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Uninstall the tank too ?0
-
If you have a way to close it off from the rest of the system and drain it, you don't need to. Otherwise... yeah, I'm afraid so. That's why it's best to precharge it before installation.Linotapia said:Uninstall the tank too ?
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
@Linotapia I assume the pressure you are speaking about is when hot? What temperature? What size tank and how much water is in the system? What was the pressure before? Photos? What type of system radiators? baseboard?0
-
What size expansion tank?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Good morning, Yes when hot… at 189 degree, before was 20 psi. See the pics.0
-
Does the boiler need to run that hot? It would be more fuel efficient if you could cover the load with 180, maybe even 160 supply temperature.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I don’t think so, How can I low or calibrate the temperature?0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements