Purge Air from Multi Zone Boiler
TerrapinSuite
Member Posts: 2
in Gas Heating



0
Comments
-
still having this issue, any advice?0
-
Each zone has to be power purged -- at least five gpm if not more -- individually. Not sure how to do that on your system, but I suspect that there are combinations of valves and drains which will allow you to do that.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
You're close, may be missing one valve. That red hose bib valve on the right side of the boiler could be your purge for all zones, however there needs to be a valve to the left of it. I can't see all the return piping to the boiler connection, is there a valve somewhere in that 1-1/4 black pipe? Like the yellow handled one above the red handled hose bib?
If so, shut off that return valve, close all the valves above the pumps, open one at a time, purge until bubbles stop. It can take 15 minutes or so on some zones. Shut off the purged one, move to the next. Open one zone iso flange at a time, purge from the red valve.
If not, where the lower most black coupling is, should be a ball valve. A sawzall, union, valve, and some nipples could add one.
Your fill valve has a fast fill function by lifting the lever on top.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.8K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 106 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 104 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 953 Plumbing
- 6.3K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements