System 2000 Frontier: What causes water in lines to have black water?
Eagle1jj
Member Posts: 2
in Oil Heating
Hi, I'm new to this site. Frank and Lindy Plumbing of Westchester County, NY Installed a new System 2000 oil fired hot water system about 12 years ago. Now they are out of business. Every copper or steel pipe they installed leaked. Possibly because they didn't properly apply dope over the teflon tape. Yesterday a plumber replaced all the piping and fittings. When he dismantled the pipes, many showed signs of black water and a muddy substance which is probably rust residue. Is there any chemical I can add to the water to help clean out the system? Any help would be appreciated.
0
Comments
-
No chemical, really -- best idea is to flush them like mad. Then purge. Then install a good magnetic filter -- most of what you see is probably magnetite from the steel pipe, and a magnetic filter will trap that. Of course, you'll have to clean that from time to time.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I would flush it, then add a hydronic cleaner, run it hot for a day, flush out the cleaner and fill with good water
Good water would be below 12 gpg, low TDS see if the manufacturer has a water spec
Then add a hydronic conditioner to protect the cleaned metals
You can buy easy to use aerosol kits
Hopefully the system is leak free, you do not want to keep adding fresh water to a closed loop hydronic system. Especially one with ferrous metals
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
What Hydronic cleaner and conditioner do you recommend? Appreciate your help. Thank you.0
-
What was it filled with originally?
I like the Rhomar or Fernox brands. they are blended specifically for hydronic work. You can get test kits to check the fluid every few years
Its wise to use the same brand cleaner as the inhibitorBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 912 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements