Question on install of hot water garage ceiling unit heater
DIYCharlie
Member Posts: 13
I am a DIYer installing a Modine horizontal hot water ceiling unit heater in the garage. The water will be supplied through a dedicated zone. I was going to use a Honeywell round (2 wire) t-stat like the house zones use. Unfortunately, I hadn't been thinking about what tells the fan to come on, but I am now.
The manual doesn't provide much guidance. The label on the connection box on the unit says something about a line voltage t-stat. Appreciate any enlightenment on how this has to be set up.
Thanks much.
The manual doesn't provide much guidance. The label on the connection box on the unit says something about a line voltage t-stat. Appreciate any enlightenment on how this has to be set up.
Thanks much.
0
Comments
-
-
The thermostat turns on the pump . Use a "B or reverse" aquastat ,which makes on temperature rise, mounted on the return pipe , The B turns on the fan when unit heat up . Normally run line voltage
There was an error rendering this rich post.
0 -
O.K., I just started looking at aquastats for the fan. Seems like the strap-on type should work, correct?0
-
A simple snap disc type on the hot supply at the heater
you can get adjustable of fixed temperature there are are limit and fan version
the fan version makes in temperature riseBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Recently installed one of these. Works fine. Not sure if it was the best option.
https://www.supplyhouse.com/Ranco-ETC-111000-000-Single-Stage-ETC-Temperature-Control-w-8-Sensor-120-240V-Input0 -
-
@DIYCharlie
Most use the thermostat to start the circulator and or boiler depending on how the boiler is operated. Then use a strap on aquastat L6006C to power the fan when the supply pipe gets hot although there are cheaper options such as what @hot_rod posted.
If the garage can get below freezing, then that has to be considered. A heat exchanger off the boiler with glycol is the best but it gets pricy with everything you need.
1 -
-
You can use an aquastat on the pipe or you can use a relay controlled by the thermostat. The relay is probably cheaper but it will blow cold air until the hot water gets there from the boiler. Could use a time delay off the thermostat to avoid the cold air.
Or you can control it all off a Crestron processor like i did.0 -
-
I suppose it would depend on the temperature setting of the the switch
If you put it on the return, you might use a lower temperature setting
First you need to decide on the SWT
ODR would complicate that.
Myson kick heaters come with a 120- 105 clip on switch
The switch would need to work down to the lowest SWT, however that is controlled
Electric water heaters and many furnaces are controlled with those reliable , inexpensive snap disc switches, they work well
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I always install them on the return and set them to 120* , so it would not blow cool air .
There was an error rendering this rich post.
0 -
I bought the below strap-on control that will make on temperature rise.
The garage will only get below freezing if utility power goes out and my generator doesn't work. I'm not using anti-freeze, so in that situation the house will also be freezing, and I suppose I will be scrambling to drain everything and sitting in front of the fireplace.
Thanks for the help all.
Johnson Controls A19DAC-1C
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements