I ran into this situation in a condo building I do consulting for. Would any of the plumbers out there be willing to weigh in on the situation? Basically, a contractor tied a washing machine into a dry vent stack that is capped off the bottom for future use. When the washer discharges, the water finds its way (sometimes) through the vanity vent on the floor below. What are the code implications of turning the dry vent into a wet vent?
TIA
Carl
TIA
Carl
"If you can't explain it simply, you don't understand it well enough"
Albert Einstein
Albert Einstein
0
Comments
-
The UPC is pretty specific on wet venting and what you have there wouldn't fly. Clothes washers are 3 fixture unit fixtures and max on a wet vent is 2 fixture units. There are fixtures on different stories using the vent (not allowed) and there are more than 4 fixtures vented.
Would it work? I don't feels comfortable saying yes on this one. When the clothes washer is discharging, it would very likely disrupt proper venting of the other fixtures and cause some traps to be siphoned.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab2 -
-
-
Misdemeanor...felony...Easy...Doing something shady with Natural gas, yes. I'm going to take a good look now. Mad Dog 🐕0
-
How close is the washing machine to the lav @Zman ?0
-
Yeah...A clothes washer is pushing it on the D.F.U.s (Drainage Fixture Units). On high rises in NYC we sometimes dump a small load like a Drinking fountain down on every floor in to a Vent stack to flush scale over the years. We call it "Washing the vent stack."
That being said, Clothes washers waste Hair, Lint, Strings, et cetera in to the waste line. This will eventually become a stoppage issue IN THE VENT STACK! This could cut air flow to many other fixtures and cause big drainage problems.
Additionally, tying in to The "suds pressure zone" can cause Soapy foam showing up in fixtures, unwanted. NYS & NYC code (ICC-based) wants one full sized stack from the base of the Main horizontal building house drain FULL size through to the Roof vent (outside air). This is where we start our Vent Stack in multi-story Buildings.
If you can, I'd drop a Dedicated 3" Vented Waste Stack for the Clothes washer and tie it in as far away from the base of the drop in the basement as possible, 40 Pipe diameters is good. Good Luck Mad Dog 🐕
3 -
Danny Scully said:How close is the washing machine to the lav @Zman ?"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Putting it next to the lav isn’t feasible, right @Zman?0
-
I was under the impression that clothes washers we only supposed to be tied into the building drain.
Cant tie into a wet vent or dry vent or bathroom group....
Yes I can see that would be a real pain in that situation.
0 -
CorrectDanny Scully said:Putting it next to the lav isn’t feasible, right @Zman?
"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
@Zman, It’s also not near that 2” or 3” waste line right? How feasible is it to actually run another line?0
-
In NYS, the only real rules on it that matter is that The Branch drain is connected to a Minimum of a 3" Drain OR you can dump in to a Slop Sink. So, I always use a 2" Washing Machine Standpipe, 2" Trap and as soon as I can get it in to a 3" Drain.
I wouldn't really call that Text book "Wet Venting" dumping in to a Vent stack.
Wet venting is using the waste of an adjacent fixture as a vent for said fixture...i.e., using the vertical Lavatory waste as the "Wet" Vent for the Bathtub 🛀 . Mad dog 🐕1 -
-
Is it code compliant?
Or will it work safely?
Which answer do you want
Search around and you can find the code and the also interpretation version of the code. Which better explains the intent. Interpretation is in blue print, typically.
https://forms.iapmo.org/email_marketing/codespotlight/2020/june4.htmBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 912 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements