Hello new here.
wondering if some can steer me in the rite direction and some pointers on a new heated driveway addition.
wondering if some can steer me in the rite direction and some pointers on a new heated driveway addition.
Im renovating the driveway and front entrance of my house and wondering if I could add a snow melt to my system with heat exchanger on a combi boiler I’ve installed last year. I’ve attached a diagram I grew up plus my existing boiler I installed.
I plan to use
I plan to use
bell&gosset 225k btu heat exchangee
tekmar 654 thermostat outdoor temp sensor and slab sensor
taco controller
tekmar 654 thermostat outdoor temp sensor and slab sensor
taco controller
0
Comments
-
Your plan looks doable. I assume that you have just left out the air sep, ex tank, and other parts you need on the SM side for clarity.
The issue you will run into is that the snowmelt will drag the boiler (and your house's heat) way down when it first fires up. It is also a good idea to limit how hot the slab can get.
If you put a motorized 3-way mixing valve controlled by the 654 on the boiler side of the heat exchanger, you will be able to prevent the boiler temps from being pulled down using the boiler return temp protection setpoint and prevent overheating using the max slab temp setpoint"If you can't explain it simply, you don't understand it well enough"
Albert Einstein2 -
-
-
700 sq ft of snowmelt could easily gobble up 100,000 btu/ hr
so you need that capacity above the heat load if you will not get much melt. It could take an hour or more just to ramp up to melt temperatureBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
It looks like he has 100 K/btu to spare. I think that the cold slab will draw it much more than that at startup. Tekmar used to make a controller that allowed you to set a delta T on the snowmelt side as well.hot_rod said:700 sq ft of snowmelt could easily gobble up 100,000 btu/ hr
so you need that capacity above the heat load if you will not get much melt. It could take an hour or more just to ramp up to melt temperature"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 912 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements