American Standard boiler and outdoor reset: Am I doing this right?
Comments
-
I didn’t know that you could connect an outdoor sensor to a 518. If so, does that influence the stat? And if so, you shouldn’t have that and the PC 700 both trying to work off of outdoor temperature.
What’s the CPH rate on the 518?Bob Boan
You can choose to do what you want, but you cannot choose the consequences.1 -
Thanks! I started thinking that myself. I'll bet it does influence it. I got carried away with gadgets and hooked an outdoor sensor to the 518. Think I will unhook it and see what happens. Couldn't find the CPH rate yet, just that it has auto cycling.Ironman said:I didn’t know that you could connect an outdoor sensor to a 518. If so, does that influence the stat? And if so, you shouldn’t have that and the PC 700 both trying to work off of outdoor temperature.
What’s the CPH rate on the 518?0 -
-
I agree, it really needs tightened up. Working on it a little at a time.0
-
Alright, I'll get some pipe insulation for it. All I had was the wall kind at the time.0
-
-
It could be exactly that. I seem to remember it having a setting for outdoor in the menu. But I'm going to unhook it anyway. Thanks for the help!0
-
-
PID thermostat control of a control doing ODR might be an over complication. Long firing times (read not cycling) requires firing rate staging or variability. I'm betting you don't have that. The very small percentage of efficiency gain achieved by lowering the water temperature might be negated by causing more short cycling. You don't want to condense your combustion by products (exhaust). ODR can help with indoor comfort in that you can control indoor over shooting and at the same time experience less undershooting when it's very cold out.1
-
I had the PC700-2 set close to the factory settings at first. All temps Fahrenheit. Boiler start 75, Outdoor start 75, Boiler design 170, Outdoor design 10, Boiler min 140, Differential 20, and I had warm weather shutdown off.Teemok said:518 will display OD temp. I'm not sure it does anything with that info. What are your design settings? Lowest OD temp, highest OD temp and warm weather shut down, Lowest and highest return water temp.?
0 -
Should I use a more simple thermostat than the 518? I had a new old style mercury stat with it before. It seemed to work alright after playing around with the heat anticipator.Teemok said:PID thermostat control of a control doing ODR might be an over complication. Long firing times (read not cycling) requires firing rate staging or variability. I'm betting you don't have that. The very small percentage of efficiency gain achieved by lowering the water temperature might be negated by causing more short cycling. You don't want to condense your combustion by products (exhaust). ODR can help with indoor comfort in that you can control indoor over shooting and at the same time experience less undershooting when it's very cold out.
0 -
PID works on the principle of adaptive pulsed on and off intervals. It (short cycles) as it approaches the set point so it doesn't over shoot. It learns from the past. You might be able to turn it off or make the setting so it is effectively turned off. I'll look it up. The ODR curve can help prevent overshooting. Two things adapting can cause problems. You want your boiler to fire in long cycles. On and off is inefficient. Your numbers look safe. Widening the diff would make it fire longer but also be off set point for more of the time. It's a comfort vs efficiency game of adjusting settings.
2 -
518 says pwm (pulse width modulation) That may or may not use PID. I see no adjustments. It's a good thermostat. On other PID stats I've used had adjustments. I would watch what it's doing as it approaches set point. The boiler control will prevent some short cycles as it rides its diff. As long as the boiler doesn't cool down and then fire for a short shot then cool again. Flame on and off is one cycle and cold to hot is another. Cold to hot is more of the efficiency killer than flame on and off.1
-
The manual for this unit is rather ambiguous, but ISTR every ODR control I've ever used says to put the boiler temp sensor on the supply pipe leaving the boiler, not the return line. This way it monitors the actual boiler temperature.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting3 -
-
Great information. From memory, it's been since this past spring that I had the heat on full time. But I seem to remember getting it to fire in good cycle times. Only it would come back on and fire for a couple minutes or more then shut off for a while till the next cycle. This is the 518 approaching the set point I assume. Didn't seem to do this from cold to hot. Thanks again, I'm a hardcore DIY guy but this is all new to me and I really appreciate the help.0
-
One other thing to consider is that if you have a single zone high mass system..ie converted gravity radiators.... the system already naturally resets itself due to the thermal mass preventing the system temperature from getting very high most of the year.To learn more about this professional, click here to visit their ad in Find A Contractor.1
-
Would it be better if I moved it to the supply? I can do that easy enough.Steamhead said:The manual for this unit is rather ambiguous, but ISTR every ODR control I've ever used says to put the boiler temp sensor on the supply pipe leaving the boiler, not the return line. This way it monitors the actual boiler temperature.
0 -
The ODR boiler control might cycle the boiler more on warm up when on the supply. (supply hits set-point while the return is still warming up. On the supply is tighter temperature management at the cost of a few more cycles. 6 or 1-1/2doz. Some conditions could have the return water coming back cooler than the boiler minimum. If want to assess/ find condensation points by controlling outlet temp. the supply works.1
-
Sounds like a plan to me. I'll give it a try and see what happens. I think I have a pretty good idea how the ODR works now. This forum is a great wealth of knowledge.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements