Gage Description..

Options
joe143
joe143 Member Posts: 23

Comments

  • joe143
    joe143 Member Posts: 23
    Options
    Do the settings seem right ?..This is an ancient Thatcher from when dinosaurs roam the earth 
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,026
    Options
    Very old pressuretrol .  Mad Dog 🐕 
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,026
    Options
    It depends...is there a working steam pressure Guage on that boiler?   Can you give us some pictures from about 5 feet back and all the piping?   Mad Dog 🐕 
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,567
    Options
    Settings look ok. Is that a steam vapor system?
  • neilc
    neilc Member Posts: 2,705
    Options
    looks like you're cutting in at 3 psi, and out at 4,
    too high for residential steam,
    dial the left scale down to 1, or just under,
    you will cut in at 1, and out at 2,
    what's your gage show?

    post a more general picture, floor to ceiling showing the boiler, and connected piping above, and all controls and sightglass,

    Have you serviced the pigtail ?
    known to beat dead horses
    bburdTeemokMad Dog_2mattmia2
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,567
    Options
    @neil your right I was looking at the scale wrong
    mattmia2
  • joe143
    joe143 Member Posts: 23
    Options
    What about the 2nd pic??
  • HVACNUT
    HVACNUT Member Posts: 5,844
    Options
    The second pic has an aquastat set to about 140° for domestic hot water purposes. Is there a tankless coil in the boiler?
    The other control with the valve is the low water cut off. You should run the boiler, then drain the boiler  through the LWCO valve while the burner is on to make sure it shuts off the burner when it reaches low level.
    Quid pro quo. Where's the pics?

    Mad Dog_2
  • ethicalpaul
    ethicalpaul Member Posts: 5,707
    Options
    Kilograms per square centimeter! Well we know the boiler is newer than 1850 or so!
    NJ Steam Homeowner. See my sight glass boiler videos: https://bit.ly/3sZW1el
  • joe143
    joe143 Member Posts: 23
    Options
    Yes it has a coil and it does shut off when I open the LWCO..  
    should the aquastat be left like at 140 ?? .. water is super hot especially when heat is on.. Also some mentioned Cleaning the pigtail.. but it doesn't have one..
    Thanks again 
  • joe143
    joe143 Member Posts: 23
    Options
    pics of  theof te
  • joe143
    joe143 Member Posts: 23
    Options
    Pics of the Dinosaur..  As a retired older man converting to gas is way out of my budget.. I couldn't believe what I was qouted on a boiler and water heater install... Sorry for ranting 
    Mad Dog_2
  • mattmia2
    mattmia2 Member Posts: 9,702
    edited October 2023
    Options
    When the boiler is steaming the water in the boiler is going to be a lot hotter than the aquastat setting. There should be a mixing valve on the dhw to keep it a a safe and constant temp.

    The aquastat is just a low limit to keep the boiler hot enough to make dhw when there isn't a call for domestic heating.

    That asbestos that is falling off is also an issue.
    SuperTechPC7060
  • neilc
    neilc Member Posts: 2,705
    Options
    does that gage drop back to 0 when the boiler is off?
    known to beat dead horses
  • joe143
    joe143 Member Posts: 23
    Options
    it's always around that 3 mark..
  • Alan (California Radiant) Forbes
    Options
    Thatcher Furnace Company. So, a furnace company made boilers? Or did boilers used to be called furnaces?
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • mattmia2
    mattmia2 Member Posts: 9,702
    Options

    Thatcher Furnace Company. So, a furnace company made boilers? Or did boilers used to be called furnaces?

    maybe they made roofs
    CLamb
  • joe143
    joe143 Member Posts: 23
    Options
    I set it at 1 now.. Gage reads
  • neilc
    neilc Member Posts: 2,705
    Options
    joe143 said:

    Gage reads

    ??

    known to beat dead horses
  • joe143
    joe143 Member Posts: 23
    Options

  • joe143
    joe143 Member Posts: 23
    Options
    looks like it's at 1 now.. what about scale on right side??
  • neilc
    neilc Member Posts: 2,705
    edited October 2023
    Options
    the scale on the right, that's your differential, leave it at 1,
    left scale is cut in, set to 1, the Ptrol turns boiler burner back on, (cut in), as pressure gets to or below 1psi,
    Ptrol shuts boiler off(cut out), at the addition of Cut In, and Differential,
    so,
    1 cut in, plus 1 differential = 2 cut out(burner off)

    the 1 on the gage, that's with boiler/burner off? for a while?
    known to beat dead horses
  • neilc
    neilc Member Posts: 2,705
    Options
    you should add another gage,
    a lower pressure gage,
    and lucky you, I got an easy spot for you,
    there is a misplaced vent right next to your Ptrol,
    remove that, you don't vent air from steam boilers, at the boiler,
    add nipples and a ball valve, and top it with a brandsy new working gage, right there,

    and sinse your hooked,
    go to the store here, and buy,
    We Got Steam,
    https://www.heatinghelp.com/store/detail/we-got-steam-heat-a-homeowners-guide-to-peaceful-coexistence
    it's a great primer, easy read, with lots on knowledge inside
    known to beat dead horses
  • joe143
    joe143 Member Posts: 23
    Options
    gage moved to the 2 position now..boiler off. it's been off for about an hour 
  • neilc
    neilc Member Posts: 2,705
    Options
    can you post a picture, more distant, of where that gage is,
    and of your sightglass,

    if you tap on that gage, does it jump around a bit?
    I wouldn't put a lot of trust in that old 30 psi gage,
    add another where the vent is,

    and I would unwire and remove your Ptrol, and check those nipples and 90 and into the tee to be sure that's all free breathing back into the boiler,
    take the Ptrol off and blow down into that assembly, it should be free breathing, or you need to clean and or replace those fittings,
    known to beat dead horses
  • neilc
    neilc Member Posts: 2,705
    Options
    is the boiler off because the thermostat is satisfied?
    or,
    is the Ptrol not responding/restarting the boiler?
    known to beat dead horses
  • joe143
    joe143 Member Posts: 23
    Options
    Boiler is back on had it off because I was changing filter. I put heat on and gage is at almost 6 now..I'll be ordering the book today thanks 
  • mattmia2
    mattmia2 Member Posts: 9,702
    Options
    neilc said:

    and lucky you, I got an easy spot for you,
    there is a misplaced vent right next to your Ptrol,
    remove that, you don't vent air from steam boilers, at the boiler,
    add nipples and a ball valve, and top it with a brandsy new working gage, right there,

    I think that is an ancient relief valve.
    neilc
  • joe143
    joe143 Member Posts: 23
    Options
    Gage after running for about 45 minutes.  it hasn't reached the thermostat temperature yetbut it has turn off 2 times  and restarted. is that normal.  Turns on runs for about 10 minutes a d shuts.. radiators are hot.
  • neilc
    neilc Member Posts: 2,705
    Options
    mattmia2 said:

    neilc said:

    and lucky you, I got an easy spot for you,
    there is a misplaced vent right next to your Ptrol,
    remove that, you don't vent air from steam boilers, at the boiler,
    add nipples and a ball valve, and top it with a brandsy new working gage, right there,

    I think that is an ancient relief valve.
    boogers,
    (1 ah sh!t = 10 atta boys)
    and I messed up,
    upon closer inspection, that does look like a safety valve,
    good call

    when the Ptrol nipps come apart,
    (because now we're at 6 psi, )
    an extra tee and nips can be added to allow for a secondary gage,
    known to beat dead horses
  • neilc
    neilc Member Posts: 2,705
    Options
    joe143 said:

    Boiler is back on had it off because I was changing filter. I put heat on and gage is at almost 6 now..

    I think you should check that piping leading to your Ptrol
    known to beat dead horses
    joe143
  • joe143
    joe143 Member Posts: 23
    Options
    would that cause it to keep coming on for like 5 minutes and turn off  its  done like 4 times..thermostat hasn't reached its point yet..

  • mattmia2
    mattmia2 Member Posts: 9,702
    Options
    joe143 said:

    would that cause it to keep coming on for like 5 minutes and turn off  its  done like 4 times..thermostat hasn't reached its point yet..

    The short answer is the boiler is oversized. The somewhat longer answer is that the pressuretrol is working as intended, the system reaches the pressure set on the pressuretrol and it turns the burner off. The radiators consume the steam that is already in the system and the pressure drops then the pressurtrol closes and fires the boiler again. The boiler is bigger than the system it is connected to so it is producing more steam than the system can consume.
  • joe143
    joe143 Member Posts: 23
    Options
    So that's reason.. I'm burning my life savings away..on oil..ugh..I think it's time to let it go.. You guys have any preference on brand..Everyone says mclain but I believe they're the most expensive..

    Thanks so much guys..you guys are a blessing to the old guys on here.. I'm sure to the younger ones too..lol 
  • neilc
    neilc Member Posts: 2,705
    Options
    joe143 said:

    would that cause it to keep coming on for like 5 minutes and turn off  its  done like 4 times..thermostat hasn't reached its point yet..

    ok, so, it IS cycling on pressure, not desirable, but not terrible either, 95% of steamers on here are oversized, and cycle on pressure,
    joe143 said:

    So that's reason.. I'm burning my life savings away..on oil..ugh..I think it's time to let it go.. You guys have any preference on brand..Everyone says mclain but I believe they're the most expensive..

    Thanks so much guys..you guys are a blessing to the old guys on here.. I'm sure to the younger ones too..lol 

    it is safe to say a modern, right sized boiler will be more efficient than yours,
    a lot, no, but more efficient, yes.
    and as far as McClain being expensive, ya get what you pay for,
    but don't buy a boiler name, buy an installer contractor, preferably from this site,
    https://heatinghelp.com/find-a-contractor/

    I just wrote this in another thread, but applies here now also,
    if you're entertaining quotes/proposals,

    make sure the contractor(s) measure all your radiators.
    this is the only way to be sure you're getting the appropriately sized steam boiler,
    Do not accept a boiler proposal sized to your existing boiler unless a radiator survey is done and proves the existing is right sized, (it won't be)

    this is a good 1st disqualifier for any contractor,
    ask your current company for a proposal,
    see if they need to survey your radiators,

    then from any proposing company,
    ask them for pictures of their last 2 or 3 steam installs, digitally,
    you will post them here, and get responses to appropriateness of the prior installs as 2nd qualifiers,
    known to beat dead horses
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,026
    Options
    All the Major boiler manufacturers are within reach of eachother.  WM is a great company, Peerless, Crown, Utica, but I'm partial to Burnham..Mad Dog 🐕