Need help heating my home ASAP. Please help. Thank you.
Hi everyone. I have the Navien 250 I'm a new home owner, I have a natural gas heater, attached are pictures of my boiler... I have baseboard radiators and I need to heat my house and when I turn the thermostat on, I hear the click sound but nothing is happening.. The radiators don't even turn on. What should I do? And also what valves should I have on? I feel like the problem to solve all of this is that the valve that's needed for the radiators isn't on. The thermostat is working how it's supposed to, but there's no heat going to the radiators. Thanks for helping me out. And also, occasssionally there's water that comes out of those pipes at the bottom which is why there's a bucket there.. I think that's water pressure issue, but that's okay. I looked up god knows how many videos on youtube, the manual for my boiler, thermostat and all of that stuff trying to figure it out myself and gave it the good ol college try. Thank you in advance.
Comments
-
The previous owner of your home did not show you how to operate the heating system?????????
Please provide us with more photos of your plumbing.
The hot water flow to the circulator appears to be shut off. The red handled valve should be open to allow the hot water from the boiler to flow to the circulator and the 2 zones that heat your home.0 -
-
I see what Leone sees,
2nd and last picture,
the longer red handle under the boiler, all the way to the left, needs to be parrallel to the pipe direction, it's closed now, and that your heat flow,
correct that and get back to us,
known to beat dead horses0 -
Okay I turned it on? since you said it had to be parallel
0 -
-
my thermostat is a Braeburn and yes they are. I don't see any error messages. o I just turn on the heat now? Or should I waitneilc said:in the display, it should cycle thru water pressure,
what do you see?
any error messages?
can you determine if the zone valves' circulator is running ?
are the batteries fresh in the thermostats?
please don't say NEST
cycle the power off for a minute, switch it back on,0 -
that valve that was closed prevented circulation thru the boiler,
the boiler protected itself and did not run,
you can wait longer, but, you will get colder, and further from having to make an emergency call to a local service provider if you do wait,
#wise_assing,
I would try turning it on
Yes, turn it on, and or turn up your thermostats.known to beat dead horses0 -
also should i turn off the boiler for a minute and then turn it back on?neilc said:that valve that was closed prevented circulation thru the boiler,
the boiler protected itself and did not run,
you can wait longer, but, you will get colder, and further from having to make an emergency call to a local service provider if you do wait,
#wise_assing,
I would try turning it on
Yes, turn it on, and or turn up your thermostats.0 -
try the thermostats first,known to beat dead horses0
-
are the thermostats switched to heat?known to beat dead horses0
-
and turned on?known to beat dead horses0
-
yesneilc said:are the thermostats switched to heat?
0 -
does the domestic hot water work ?known to beat dead horses0
-
I'll give it a little bit. It's not turning on rn still but the oven is being used right now so maybe it takes a little bit?0
-
are the little caps loose on the 2 brass air vents?
there's one vent on the top left corner of the boiler,
and the second is down and to the left on that balck air scoop in the piping run,
are those caps loose?
any air come from them if they were tight, and you loosened them ?known to beat dead horses0 -
No other gas appliances will have an effect on your gas boiler unless you have a gas delivery problem. You don't -Ineedhelpwithheat86 said:I'll give it a little bit. It's not turning on rn still but the oven is being used right now so maybe it takes a little bit?
0 -
if cycling the power switch does not "fix" this,
then it may be time to call for service,known to beat dead horses0 -
edit: nevermind0
-
Thank you.MaxMercy said:
No other gas appliances will have an effect on your gas boiler unless you have a gas delivery problem. You don't -Ineedhelpwithheat86 said:I'll give it a little bit. It's not turning on rn still but the oven is being used right now so maybe it takes a little bit?
0 -
Should I power cycle the boiler? Because the pipe itself is cold... not like the other one where they're warm0
-
the left most pipe with the valve you opened,
is this getting hot? or is it cold?
if the boiler is working at all, that pipe should be warming up,
the #2 left pipe is your domestic hot, I assume this one is hot,
FYI, that boiler will only do domestic, or heating , at any one time,
noone is taking a long hot shower right now, correct?known to beat dead horses0 -
neilc said:
the left most pipe with the valve you opened,
is this getting hot? or is it cold?
if the boiler is working at all, that pipe should be warming up,
the #2 left pipe is your domestic hot, I assume this one is hot,
FYI, that boiler will only do domestic, or heating , at any one time,
noone is taking a long hot shower right now, correct?
They were. But now they're not. They just finished taking a shower. So i should try it now? Since it shows both SH and PHW to be off0 -
it won't hurt to cycle power,
but I think if you have hot domestic, a power cycle is not your answer,
there are other parts, valves and a circulator, inside that boiler,
It may be time to call service,
where are you located?
https://heatinghelp.com/find-a-contractor/known to beat dead horses0 -
how do i turn the circulator on or should it already be on0
-
the boiler circ is controlled internally by the boiler,
(call service)
the system circ is controlled by that green taco box, left of the boiler,
if your thermostats are on, and calling for heat, there should be more lights lit under that green one on top,
how many lights lit on the green taco?
any chance those thermostats are new, like this past summer?known to beat dead horses0 -
i don't think so we just moved into the place like 3 months agoneilc said:the boiler circ is controlled internally by the boiler,
(call service)
the system circ is controlled by that green taco box, left of the boiler,
if your thermostats are on, and calling for heat, there should be more lights lit under that green one on top,
how many lights lit on the green taco?
any chance those thermostats are new, like this past summer?0 -
so how many lights on the taco ?known to beat dead horses0
-
0
-
and then on top there it says 1f and B0
-
taco says one zone calling for heat, and its valve is open,
any noise, or warmth felt from the circulator? is it working?
try switching that speed control to low, to medium, and back to high,
any noise? whirring?
and was that left pipe warm under the boiler?
cuz if not, then this circ working or not won't have heat to push around the house,
really time to call a service tech.known to beat dead horses0 -
Yeah I think I'm going to have to call a service tech or something. Tried pretty much everything0
-
let us know what was foundknown to beat dead horses0
-
The pipe is still cold unfortunately0
-
Did your home inspector run the heating system to ensure it was working before you bought it? If we know it was working 3 months ago, that could be helpful.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Update: I reset the boiler, unplugged it for 2-3 minutes and then plugged it back in and now the heat is working. Water is going to the pipe that was cold and circulating around the houseethicalpaul said:Did your home inspector run the heating system to ensure it was working before you bought it? If we know it was working 3 months ago, that could be helpful.
2 -
guess we should have tried that earlier yesterdayknown to beat dead horses0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements