Mixed hydronic and radiant, same boiler
RicD
Member Posts: 3
The hydronic heating boiler I'm working on was originally configured for 4 zones, although only 2 were used. I have added some radiant floor heating zones that will use the other 2 legs. My issue is that the 4 Taco 007 circulators are all on a manifold on the return side with no room to plumb around them. The best practice for the mixing valves needed for the radiant loops is to put the circulator on the outlet side of the mixing valve. Since the circulators are already plumbed in, I'd rather not move them. My question is, can I use a monoflo tee on the return line to feed the cold side of the mixing valve and leave the circulator in its current return/pull location?
0
Comments
-
no.
To make a mixing valve work at all, you have to pump out of the outlet (zone circulator)Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
You could use a mechanical mixing valve or injection rather than a thermostatic mixing valve, but otherwise no. Depending on the boiler, you may also need to add some sort of protection from the cooler radiant return temps if they're running without your high temp emitters.
Also, "hydronic" encapsulates all types of water heating and cooling- including radiant.0 -
Technically, it is on the outlet side. they are pull pumps on the return side. Here's a rough sketch.
0 -
The pressure drop of the radiant circuit will be higher than the pressure drop across the 3 port valve. The path of least resistance will be across the valve not thru the circuit.
So you are not really pulling thru the valve from the H&C ports.
Here are 3 options that work well for adding a low temperature zone.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream2 -
You will need to move the pump for that low temperature zone. No Ands, Ifs or Buts if you are going the thermostatic mixing valve route. But that is not the end of the world. Select a convienent location for the mixing valve and place the pump on the outler side of the mixing valve. then just use a circulator flange to connect to the existing circulator flange with a gasket and 2 bolts. That will end up being an impromptu union of sorts.
Here is my impression of what you are dealing with. And the way to deal with it
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
You can pump through an un-powered circ also, leave the one in, remove the internal check if it has one, add another circ after the mix.
The jumper Ed shows can be easily made with two sweat flanges and a piece of copper tube.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Also, the sketch the OP posted. with the mixing valve.
I always thought a "mixing Valve has two inlets and one outlet and a diverting valve has 1 inlet and two outlets.0 -
So, I guess it's inevitable I have to move the circulator. Thanks for the comments. Much appreciated.0
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 925 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements