One pipe boiler system
4124526230
Member Posts: 1
The main run is 1.25 can I add 12ft of baseboard using 3/4 and how many feet can I go
0
Comments
-
You question is somewhat vague. Are you saying that you have a Monoflo system with a 1.25” main? And are you asking if you can add 12’ of BB that’s teed off of that main or are you asking if you can run the 1.25” main directly through the BB? The answer to the latter would be no.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
You may add whatever you want. The question remains will it do what you want?0
-
12 feet of baseboard only needs about .7 gpm. You can use 1/2 Inch branches to the new baseboard. Space the tees 12" or more apart do not put them close together. Use a regular tee on the supply pipe and a Monoflo or venturi tee on the return. Don't forget to install an air vent.
using 3.4" might steel some heat from another room.
Pitch the branches from the main to the baseboard up slightly if possible.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements