New Nozzle
joe143
Member Posts: 23
in Oil Heating
Hello folks- Just did a cleaning of my old thatcher boiler. Put in new filters .Switched out the nozzle from a 1.00/80 to .75/80 trying to save money on fuel..but it started blowing smoke from chimney..Thoughts?
0
Comments
-
White smoke I assume , go back to a 1.00 80* W nozzle
There was an error rendering this rich post.
0 -
Not a pro here, but if we look at it in the simplest form you reduced the amount of fuel but have the original amount of air entering the combustion chamber. Imho lean and hot, possibly dangerous ?
Likely not a good idea unless someone with combustion gauges readjusts the air settings, and possibly the fuel pump pressure ?
30+ yrs in telecom outside plant.
Currently in building maintenance.1 -
@joe143
If you change to a different size nozzle you also change the firing rate (amount of oil burned). It's just like a car once the fuel rate is adjusted now the air needs adjustment.
Now since you messed with it you need a technician with a combustion analyzer to set the burner up properly.
If not, you could soot the boiler up (if your lucky) or have a delayed ignition or other serious problem if your not lucky1 -
If you change the nozzle, you must make sure that the new nozzle is the correct pattern for the boiler. Just making it smaller won't do. Then you must perform a complete combustion test and get the air and pressures correct. This requires instruments which you may or may not have.
And that said... changing the firing rate for the boiler, even if you can get it right, is NOT going to reduce your fuel use. Sorry. Your house loses a certain amount of heat all the time, and the boiler needs to burn a certain fixed amount of fuel to produce that heat. All that reducing the firing rate will accomplish is that the boiler will have to run longer to make you warm enough.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England3 -
Thanks!0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements