Softener, PRV, Expansion Tank
Comments
-
It probably is normal -- it depends entirely on the acceptance volume of the expansion tank relative to the volume of the water heater. In your case, I'm guessing that the expansion tank is the cute little thing teed off the water heater. That will tend to reduce water hammer, particularly in the lines connected directly to it, but it's much too small to control pressure variations caused by temperature changes in that big water heater.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
I guess I am confused why I wasn't seeing these fluctuations before the new tank. The old expansion tank was exactly the same size and brand. It had been installed horizontally which the plumber thought had initiated the failure. I'm just concerned about continued pressure building. I'm just unsure if I need to call them back out or not. Maybe this is typical for my current setup. 🤔0
-
You need to know what the pressure is in the expansion tank WITH THE WATER DRAINED
out of the bladder tank, a lower air pressure will allow for more compression of the air in the
expansion tank with a greater acceptance volume and a quieter potable water supply.
They should have installed a shut off/drain valve under the bladder tank also.2 -
Was the gauge there before all of this started?
Pressure can and does fluctuate differently under many different circumstances. You might be experiencing "normal" occurrences.0 -
Yes. The gauge has been there since the softener was installed 3 months ago. It is built into the softener system. I don't hear any sounds from anything. I don't even hear when the water heater is in heat cycle, just guessing since after a large use if hot water is mostly when I see the psi rise. Just seeing the fluctuation. Everything seems to be normal with pressure at any fixture in the house. I just can't see why it would have solved the hammer but started the fluctuations.0
-
If the PRV failed after 3 years I'd put a really good strainer ahead of it to catch any garbage that may get stuck in it or damage it. Something with a good 80 or 100 mesh strainer in it. Most brass and bronze strainers come with a 20 mesh, but they usually have an option for the finer 80 ones.
I know it's a separate subject, but figured I'd mention it.
As far as 70 and dropping to the high 50s, that's likely very normal due to how the PRV operates. You're going to have a small range in pressure as the valve needs this drop in order to open further. I wouldn't be surprised if it drops to the low 50s under heavy flow.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
So if it gets up to 70 after heating, and say I were not to be home using any water for a couple of days, it won't just keep rising on top of that will it? I'm guessing it drops even if I don't open a faucet or flush? Sorry, I'm paranoid about this. I look at it 20 times a day.0
-
Wait I just re-read your original post.SG17 said:So if it gets up to 70 after heating, and say I were not to be home using any water for a couple of days, it won't just keep rising on top of that will it? I'm guessing it drops even if I don't open a faucet or flush? Sorry, I'm paranoid about this. I look at it 20 times a day.
You're 100% that the pressure goes up from the water heater?
I assumed you meant it was 70PSI with nothing running, and 57 PSI with stuff using water.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Check the incoming pressure. PRV want a 2:1 maybe 3:1 pressure reduction. If main pressure is over 150, psi two PRVs in series
High incoming or spikes destroy PRVs
A water hammer arrester at the softener may be a good add onBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I assume the water heater. It is set at 57. Drops to 50 when using water and will go to 70 seemingly after a lot of hot water has been used or a couple of random times throughout the day. I literally can barely open a faucet for 2 seconds and it drops back to 57. I don't hear the water heating so I can't be sure, but it seems to be from that based on the timing.0
-
I have tried a 2 hand gauge on an outdoor spigot. The black hand was always at 57 when the softener gauge was at 57. The red hand would go from 80-120 max, but I can't be sure how accurate it was. I never saw the black hand change. Ugh....0
-
45- 60 psi is plenty for a home. Plumbing fixtures are rated to max. 80 psi.
The pressure you measure with nothing running in the home is static pressure, set the PRV to 60 with nothing running.
The pressure as you start flowing things, dynamic pressure, will drop. This is called fall off pressure.
Ideally with everything in the home running a 7- 10 psi fall off is rule of thumb. If it drops 10 psi with one fixture running, a plugged strainer, valve not completely open, failed prv. Or some other obstruction in the main piping.
Pressure creep is either lack of working thermal expansion device, or a PRV leaking by.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Thanks everyone for your insight. Going to call the plumber to come back.0
-
My sons incoming water pressure is at 100 -120 PSI so he and I installed a name brand and expensive PRV on the supply line and set the discharge pressure at 65PSI. We also installed a water hammer arrester near that PRV in the same horizontal line. We installed an oversized expansion tank at the water heater with the air charge at 60 PSI. His PRV is now over 10 years old and working fine. The water pressure fluctuates by 5-10 PSI depending on the demand. He has never seen the system pressure exceed 70 PSI.0
-
Thanks for the info. This morning my gauge read 70. Turned on a faucet and it dropped to about 48, then rose to 56. It soon returned to 70 and then dropped to 66 about an hour later with no water having been used. I'm so perplexed by this. If the new PRV and new ET are set to 58ish I just assumed it would stay there when no water is being used. My old PRV and ET were not fluctuating, I just had suddenly got hammer in expansion tank. I'm so reluctant to call them back. The items they installed have 5 years warranty through them. I'm just concerned they will tell me it's another faulty item needing replaced in a house under 3 years old. 3 PRVs and 2 ETs in that amount of time already seems hard to process.
0 -
-
My first guess was they didn't properly precharge the tank so it's waterlogged and not doing it's job, much.SG17 said:Is it possible they have set the expansion tank at a higher psi allowing the pressure to rise to 70 even though the PRV is at 58?
Also, what size water heater is that? It looks rather large.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment2 -
The water heater is 50 gallon. The expansion tank definitely sounds hollow when knocking at the top vs the bottom. I know they added air with a pump to the tank when they put it on but I never asked any questions regarding the psi. I had not mentioned, though it seems irrelevant, all the copper plumbing in the photos was installed with the new tank. It had braided flex and pex before. For a girl, I'm having to try way too hard to figure this out. Don't have a lot of plumbing knowledge and I'm concerned that's putting me at a huge disadvantage. I don't feel like the fluctuations are hurting anything I just don't feel like it should be performing this way.0
-
I agree with @ChrisJ . The plumber needs to remove the expansion tank or isolate and drain it then and only then check the air pressure in the tank.
The air pressure in the tank should then be adjusted to see the same pressure the prv puts out and a gauge should be installed on the system. The reinstall the tank with the adjusted pressure.1 -
You could probably shut power and water off to the tank. Drain a little water to get to 0psi and set the bladder pressure.Ideally the tank should have a valve setup to isolate it and allow pressure to be released. It should be checked annually.The bladder needs to be set with enough pressure to balance the water pressure at setpoint. So it has some headroom to collapse progressively as the pressure goes above setpoint. If the pressure is not high enough it may be have compressed at setpoint leaving little room to account for thermal expansion or regulator fluctuations. If the bladder is collapsed a small amount of expansion can cause a big pressure change since there is no where for the added volume to go but to slightly expand/stretch anything that gives.Also agree on adding a strainer upstream of the regulator.Some tanks like to be oriented different directions depending on the style of bladder. And will last longer in the recommended orientation.0
-
Ah... very helpful. Besides the pressure tank, you mention in passing that " all the copper plumbing in the photos was installed with the new tank. It had braided flex and pex before". A useful object lesson in never overlooking anything that changed between when it worked and when it didn't. That flex and pex was absorbing a lot of the water hammer and pressure change -- quite possibly all of it -- and the copper can't.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
No,Jamie Hall said:Ah... very helpful. Besides the pressure tank, you mention in passing that " all the copper plumbing in the photos was installed with the new tank. It had braided flex and pex before". A useful object lesson in never overlooking anything that changed between when it worked and when it didn't. That flex and pex was absorbing a lot of the water hammer and pressure change -- quite possibly all of it -- and the copper can't.
But that expansion tank should be absorbing a lot of it, off the top of my head that tank is more than big enough for a 50 gallon heater.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
I confirmed today that the rise is definitely happening when the WH heats and it does return to the set psi after it cools. One person had suggested this may be normal. I feel like the plumber should have mentioned if this was something I would see happening. Won't be able to have them come back for a week or two. Just gate to pay another trip fee. I'm already $$$$ in on this.0
-
I'm not sure if I had suggested it or not, but no, I don't feel that's normal with a properly working expansion tank.SG17 said:I confirmed today that the rise is definitely happening when the WH heats and it does return to the set psi after it cools. One person had suggested this may be normal. I feel like the plumber should have mentioned if this was something I would see happening. Won't be able to have them come back for a week or two. Just gate to pay another trip fee. I'm already $$$$ in on this.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment2 -
Too many variables, @ChrisJ . The pressure will always rise in a closed system when the water is heated. The question is... how much, and how much is "normal". It depends on the total volume of the water being heated, the initial and final temperatures, the initial pressure, the expansion volume available in the tank and the air pressure in the tank at the start... water heaters (as contrasted with boilers) are problematic, as there is a comparatively large volume of water involved, the delta T is large, and the initial pressure is usually rather high again compared to a boiler. All of which mean that a surprisingly large tank is required to keep the pressure change small.ChrisJ said:
I'm not sure if I had suggested it or not, but no, I don't feel that's normal with a properly working expansion tank.SG17 said:I confirmed today that the rise is definitely happening when the WH heats and it does return to the set psi after it cools. One person had suggested this may be normal. I feel like the plumber should have mentioned if this was something I would see happening. Won't be able to have them come back for a week or two. Just gate to pay another trip fee. I'm already $$$$ in on this.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Jamie Hall said:
Too many variables, @ChrisJ . The pressure will always rise in a closed system when the water is heated. The question is... how much, and how much is "normal". It depends on the total volume of the water being heated, the initial and final temperatures, the initial pressure, the expansion volume available in the tank and the air pressure in the tank at the start... water heaters (as contrasted with boilers) are problematic, as there is a comparatively large volume of water involved, the delta T is large, and the initial pressure is usually rather high again compared to a boiler. All of which mean that a surprisingly large tank is required to keep the pressure change small.ChrisJ said:
I'm not sure if I had suggested it or not, but no, I don't feel that's normal with a properly working expansion tank.SG17 said:I confirmed today that the rise is definitely happening when the WH heats and it does return to the set psi after it cools. One person had suggested this may be normal. I feel like the plumber should have mentioned if this was something I would see happening. Won't be able to have them come back for a week or two. Just gate to pay another trip fee. I'm already $$$$ in on this.
So.
How do we calculate how much 50 gallons (extreme situation) will expand when heated from 40F to 140F?
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
The expansion tank is on the cold side of the water heater. Is there a heat trapping nipple or check valve on the cold inlet?0
-
You wouldn't think so from the factory as most of them rely on the city water (without PRV etc) or well tank for expansion purposes.WMno57 said:The expansion tank is on the cold side of the water heater. Is there a heat trapping nipple or check valve on the cold inlet?
Though, now that you mention it, it looks like they did use dielectric unions which isn't necessary on a Bradford White and in my opinion, would likely cause more issues than they solve. But that's a totally different subject.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Use the Amtrol Net Expansion of Water tables 40- 180° the factor is .02763 X 50= 1.38ChrisJ said:Jamie Hall said:
Too many variables, @ChrisJ . The pressure will always rise in a closed system when the water is heated. The question is... how much, and how much is "normal". It depends on the total volume of the water being heated, the initial and final temperatures, the initial pressure, the expansion volume available in the tank and the air pressure in the tank at the start... water heaters (as contrasted with boilers) are problematic, as there is a comparatively large volume of water involved, the delta T is large, and the initial pressure is usually rather high again compared to a boiler. All of which mean that a surprisingly large tank is required to keep the pressure change small.ChrisJ said:
I'm not sure if I had suggested it or not, but no, I don't feel that's normal with a properly working expansion tank.SG17 said:I confirmed today that the rise is definitely happening when the WH heats and it does return to the set psi after it cools. One person had suggested this may be normal. I feel like the plumber should have mentioned if this was something I would see happening. Won't be able to have them come back for a week or two. Just gate to pay another trip fee. I'm already $$$$ in on this.
So.
How do we calculate how much 50 gallons (extreme situation) will expand when heated from 40F to 140F?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
The coefficient of expansion of water is variable, but 0.0005 is a good first approximation. So, in your instance, it would be about 2.5 galloons.ChrisJ said:Jamie Hall said:
Too many variables, @ChrisJ . The pressure will always rise in a closed system when the water is heated. The question is... how much, and how much is "normal". It depends on the total volume of the water being heated, the initial and final temperatures, the initial pressure, the expansion volume available in the tank and the air pressure in the tank at the start... water heaters (as contrasted with boilers) are problematic, as there is a comparatively large volume of water involved, the delta T is large, and the initial pressure is usually rather high again compared to a boiler. All of which mean that a surprisingly large tank is required to keep the pressure change small.ChrisJ said:
I'm not sure if I had suggested it or not, but no, I don't feel that's normal with a properly working expansion tank.SG17 said:I confirmed today that the rise is definitely happening when the WH heats and it does return to the set psi after it cools. One person had suggested this may be normal. I feel like the plumber should have mentioned if this was something I would see happening. Won't be able to have them come back for a week or two. Just gate to pay another trip fee. I'm already $$$$ in on this.
So.
How do we calculate how much 50 gallons (extreme situation) will expand when heated from 40F to 140F?Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Most tanks have heat trapper nipples, either a rubber flapper or plastic ball inside. I don't think they are a "bubble tight" seal, so the pressure would bleed through to the tank. I can blow through this one, the flapper is a bit smaller than the ID of the nipple.ChrisJ said:
You wouldn't think so from the factory as most of them rely on the city water (without PRV etc) or well tank for expansion purposes.WMno57 said:The expansion tank is on the cold side of the water heater. Is there a heat trapping nipple or check valve on the cold inlet?
Though, now that you mention it, it looks like they did use dielectric unions which isn't necessary on a Bradford White and in my opinion, would likely cause more issues than they solve. But that's a totally different subject.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream2 -
Oops. Read the wrong value for expansion -- that's the Celsius value. The Fahrenheit value is 0.0003, the volume is 1.5 gallons. Still a fair amount.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 912 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements