Where to Put main vent ?

G_thehelpernyc
G_thehelpernyc Member Posts: 3
edited October 2023 in Strictly Steam
I have a 10 unit 5 floors apt building  in bronx. one pipe steam with 2 mains 2.5 inch serving 3 2 inch risers each. I currently don’t have main vents on the mains and looking to install a Gorton 2. The mains run 30 ft from the boiler to end of main. I am having issues with heating not reaching the last floors. These are picture of both ends of mains


Comments

  • neilc
    neilc Member Posts: 2,854
    this last picture shows a "main" atop that left most tee,
    is there another in those back dark shadows ?
    this main is too small,
    I see a bushing, which when removed, could fit a larger vent,
    what's in the shadows?
    known to beat dead horses
  • neilc
    neilc Member Posts: 2,854
    and have you looked at the tops of those risers?
    could / should be vents up there,
    known to beat dead horses
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,518
    Could be a puddle, but when you have plenty of Steam Available its going to blast in to the puddle & past it toward the point of lower pressure, the rad or main vent.  Mad Dog 🐕 
    G_thehelpernyc
  • Jamie Hall
    Jamie Hall Member Posts: 24,842
    neilc said:

    and have you looked at the tops of those risers?
    could / should be vents up there,

    This. If you can put some good big main vents at the tops of the risers, you almost certainly will see an improvement.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    Mad Dog_2
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,470
    You may need to drill and tap to put vents on. You probably could use vents on the tops of the risers as well. Probably was designed for coal originally so it probably had few if any vents.

    If you could post a sketch of the piping in the picture and mark where the pipes go it would be easier to decide where to put the vents.
    Mad Dog_2
  • G_thehelpernyc
    G_thehelpernyc Member Posts: 3
    So each side the building has 3 riser coming off the main. One 2 inch for the bathrooms running straight up . Another running straight through the bedrooms and suppying a radiator on other side of wall in kitchen. The third riser runs straight up Also straight pipe on one side and supply radiator on other side of wall. The 2 riser are exposed on the last floors and have Gorton D radiator vents tapped on the pipe. The 3rd riser on the last floor changes instead being straight pipe in bedroom is instead supplying 2 radiator back to back rooms
  • G_thehelpernyc
    G_thehelpernyc Member Posts: 3

  • Jamie Hall
    Jamie Hall Member Posts: 24,842
    The Gorton D is a nice vent. It's not a main vent. Swap them out for Gorton #2s on the risers (not on the radiators -- leave the radiator vents alone to control the radiators).
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    Mad Dog_2
  • dabrakeman
    dabrakeman Member Posts: 645
    Looks like the main in your first pictire is setup parallel flow with an existing main vent at end of the main extension.  Easy enough to increase that venting but that only addresses 30 ft in a 5 story building.  The other main probably would require drill and tap.  As @nelic and @Jamie say biggest improvement would be if can get main vents at the top of the risers.