New Main Vents

Options
2»

Comments

  • bergensteamguy
    bergensteamguy Member Posts: 57
    edited October 2023
    Options
    Tapped the first main 1/2 hole with all brass fittings and Gorton #2. Did an initial test for leaks, and it was leak free! Going to see how this affects heating performance. I put in a tee in case I need another #2.


    Spin
  • bergensteamguy
    bergensteamguy Member Posts: 57
    Options
    Update @Mad Dog_2 & @ethicalpaul. I fired up the boiler with the additional Gorton #2 venting. The radiators are heating up much faster and almost perfectly even. Thanks for the help!
    Spin
  • JUGHNE
    JUGHNE Member Posts: 11,088
    Options
    It looks like that main slopes down towards the right?

    Although you have a very short length of horizontal brass piping there, it too should be such that any water will drain back into the main.

    If you add a tee and extend the brass then you might want to consider rotating the riser 180 degrees.
  • bergensteamguy
    bergensteamguy Member Posts: 57
    Options
    Hi @JUGHNE, its a tricky photo. The main actually is pitched to drain to the left of the picture. The horizontal brass piping is actually pitching in the same direction as the main, so any condensate should flow in the same direction. The nipple is 6 inch. I felt that was high enough given the additional height of the elbow and tee...
    Spin