Why does my gas Burnham boiler turn off after a few minutes?

Mike8787
Mike8787 Member Posts: 1
New Home 

Gas Boiler will not 
Start using only the thermostat 
Need to put match to pilot light 

When it does ignite 
It stays burning for only a few minutes 
Dirty Hot water blows out of the “ bleeder faucets “ and 
The flame goes out 

We tightened the bleeder valves 
We have three zones 
All three valve controls are 
Open 
All the water lines are open 

When the machine runs 
The pipes below the 
Valve controls are hot 
But above they are not 

We have an argo control panel 
Three green lights on top 
Three red lights  below 



Comments

  • Steamhead
    Steamhead Member Posts: 17,387
    Bad circulator? Where are you located?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Ironman
    Ironman Member Posts: 7,555
    It sounds like multiple issues.

    ”Match under pilot.” That sounds like a bad thermalcouple.

    ”Pipes hot below, but not above.” That could be a bad circulator as Steamhead mentioned. Or it’s air bound. Or the static fill pressure is too low.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • realliveplumber
    realliveplumber Member Posts: 354
    Looks like the ball valve before the pressure reducing valve is closed. (No backflow preventer visible in the typical location either')